Re: [EnergyPlus_Support] diffuse and direct solar



Dear Linda,

you are are right.
If I perform my simulation with a time step of one hour, then solar radiation outputs
exactly match the inputs in the weather file.
If I use a smaller time step and ask for hourly reported solar radiation data,
they don't match the input.

Thank you very much

Adriana Angelotti

 
At 09.29 18/11/02 -0600, you wrote:

If you use an hourly time step and reporting, you should see the same values reported.  If you are using less than hourly time steps in your EnergyPlus input, things will get a bit confusing due to EnergyPlus Weather Interpolation and the "summing" of these values when reported.

Solar radiation values have a particular problem in EnergyPlus reporting and the interpolation scheme as they are not "continuous" values (like dry bulb where not much variation happens during the course of a day) and the interpretation of the data coming from weather sources is also a bit confusing. 

....

In practice, virtually all energy analysis programs treat the incoming solar radiation as an "instantaneous" value.  This works well for hourly programs which only have one value to deal with.  EnergyPlus has a compounding problem here -- because it must determine how to break up that hourly value into several time steps (unless the time step input is hourly).

Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team


To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/






Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/






Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.