Re: [EnergyPlus_Support] i cannot get the heating and cooling load
Ian:
You do not need a complete HVAC system to compute the heating and
cooling loads, but you do need to add a "Purchased Air" system. You
can read about this option in the Input Output Reference starting on
page 393. For an example of the objects required to describe this,
see EnergyPlus\ExampleFiles\PurchAir.idf
Mike
On 18 Nov 2002, at 22:15, Ian Yiheng Wang wrote:
> Hi there,
>
> i am using the program for buildings' heating and cooling systems
> designing. First of all i need the result of heating and cooling load
> because what i need now is the heating and cooling load alone before i
> move on to other apects of the design. i have already put in the
> nscessary data for the heating and cooling load as such, the geometry
> of buildings, the weather date, people, equipment,etc. the problem i
> have got is that i cannot view my result for the heating and cooling
> load. do i have to complete the whole processs such as the Nodes, air
> distribution, water loops, etc. to get the heating and cooling load. i
> believe that the loads are independent of heating and cooling system
> itself. kindly give me your advise on how to go about it.
>
> regards,
>
>
> Ian YH Wang
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/JjlUgA/vN2EAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/