Re: [EnergyPlus_Support] i cannot get the heating and cooling load



Yes, Purchased Air is modeled as an ideal system.  I have not tested 
various supply temperatures to confirm that it does not impact the 
reported load, but it should work within limits.  Obviously, the 
heating supply temperature must be greater than the heating setpoint 
in the zone.  Likewise, the cooling supply must be below the cooling 
setpoint.  Setback recovery is an important consideration when using 
Purchased Air.  Purchased Air will provide enough heating/cooling to 
recover from setback in a single timestep.  This is why sizing 
calculations should be done without setback.

Mike



On 20 Nov 2002, at 14:59, Adriana Angelotti wrote:

> About Ian's question a and Mike's answer on heating/cooling load :
> 
> If Purchased Air is a system you add only to compute heating and
> cooling load, the simulation results should be independent from the
> parameters you must input such as: - heating/cooling supply air
> temperature - heating/cooling supply air humidity ratio
> 
> Moreover, the thermostatic control should be ideal, that is able to
> respond immediately to temperature changes.
> 
> Are my ideas correct? Is Purchased Air an ideal system in every sense?
> Thanks
> 
> Adriana Angelotti
> 
> ----------
> Adriana Angelotti
> PhD student
> eErg end-use Efficiency Research Group
> Politecnico di Milano, Dipartimento di Energetica
> Piazza Leonardo da Vinci 32
> 20133 Milano
> Italy
> ph +39.02.2399.3859
> fax +39.02.2399.3940
> 
> 
> ----------
>   At 09.09 19/11/02 -0600, you wrote:
> >Ian:
> >
> >You do not need a complete HVAC system to compute the heating and
> >cooling loads, but you do need to add a "Purchased Air" system.  You
> >can read about this option in the Input Output Reference starting on
> >page 393.  For an example of the objects required to describe this,
> >see EnergyPlus\ExampleFiles\PurchAir.idf
> >
> >Mike
> >
> >
> >On 18 Nov 2002, at 22:15, Ian Yiheng Wang wrote:
> >
> > > Hi there,
> > >
> > > i am using the program for buildings' heating and cooling systems
> > > designing. First of all i need the result of heating and cooling
> > > load because what i need now is the heating and cooling load alone
> > > before i move on to other apects of the design. i have already put
> > > in the nscessary data for the heating and cooling load as such,
> > > the geometry of buildings, the weather date, people,
> > > equipment,etc. the problem i have got is that i cannot view my
> > > result for the heating and cooling load. do i have to complete the
> > > whole processs such as the  Nodes, air distribution, water loops,
> > > etc. to get the heating and cooling load. i believe that the loads
> > > are independent of heating and cooling system itself. kindly give
> > > me your advise on how to go about it.
> > >
> > > regards,
> > >
> > >
> > > Ian YH Wang
> > >
> > > ------------------------ Yahoo! Groups Sponsor
> > > ---------------------~--> Get 128 Bit SSL Encryption!
> > > http://us.click.yahoo.com/JjlUgA/vN2EAA/xGHJAA/dkFolB/TM
> > > ------------------------------------------------------------------
> > > ---~ ->
> > >
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >
> > >
> > >
> > >
> > >
> > > Your use of Yahoo! Groups is subject to
> > > http://docs.yahoo.com/info/terms/
> > >
> >
> >
> >
> >========================================================
> >EnergyPlus Testing and Support
> >EnergyPlus-Support@xxxxxxxx
> >


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/