About Ian's question a and Mike's answer on heating/cooling load :

If Purchased Air is a system you add only to compute heating and cooling load,
the simulation results should be independent from the parameters you must input such as:
- heating/cooling supply air temperature
- heating/cooling supply air humidity ratio

Moreover, the thermostatic control should be ideal, that is able to respond
immediately to temperature changes.

Are my ideas correct? Is Purchased Air an ideal system in every sense?
Thanks

Adriana Angelotti

Adriana Angelotti
PhD student
eErg end-use Efficiency Research Group
Politecnico di Milano, Dipartimento di Energetica
Piazza Leonardo da Vinci 32
20133 Milano
Italy
ph +39.02.2399.3859
fax +39.02.2399.3940


 At 09.09 19/11/02 -0600, you wrote:
Ian: 

You do not need a complete HVAC system to compute the heating and
cooling loads, but you do need to add a "Purchased Air" system.  You
can read about this option in the Input Output Reference starting on
page 393.  For an example of the objects required to describe this,
see EnergyPlus\ExampleFiles\PurchAir.idf 

Mike 


On 18 Nov 2002, at 22:15, Ian Yiheng Wang wrote:

> Hi there,
>
> i am using the program for buildings' heating and cooling systems
> designing. First of all i need the result of heating and cooling load
> because what i need now is the heating and cooling load alone before i
> move on to other apects of the design. i have already put in the
> nscessary data for the heating and cooling load as such, the geometry
> of buildings, the weather date, people, equipment,etc. the problem i
> have got is that i cannot view my result for the heating and cooling
> load. do i have to complete the whole processs such as the  Nodes, air
> distribution, water loops, etc. to get the heating and cooling load. i
> believe that the loads are independent of heating and cooling system
> itself. kindly give me your advise on how to go about it.
>
> regards,
>
>
> Ian YH Wang
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/JjlUgA/vN2EAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>



========================================================
EnergyPlus Testing and Support     
EnergyPlus-Support@xxxxxxxx


To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/






Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.