Alexander,

In the "Always On" case the setpoint does not have to be entered and the
default value of zero is not used.

Fred Winkelmann

Alexander Beisteiner wrote:

> Dear Sir/Madam
>
> The object WindowShadingControl requires a certain setpoint value.
> What value do I have to enter if the Shading Control Type ?Always On?
> is used. A simulation without specifying the value, produces the
> following error message:
>
> ** Warning ** Object=WINDOWSHADINGCONTROL, name=BLIND, entered with
> less than minimum number of fields.
>
> **~~~** Attempting fill to minimum.
>
> ** Warning ** Set point is zero in WindowShadingControl BLIND
>
> **~~~** This may mean set point was not specified when it should have
> been.
>
> Other than explained in the user manual, in my case the shading does
> not need to be activated as it is on all the time. So, do I have to
> set a value or do not I have?
>
> I would appreciate your help.
>
> Regards
>
> Alexander
>
> __________________________________
>
> DI (FH) Alexander Beisteiner
>
> Forschungs- und Technologietransfer
> Pinkafeld GmbH
> Steinamangerstrasse 21
> 7423 Pinkafeld
>
>
> alexander.beisteiner@xxxxxxxxxxxxxxxxxx
> http://www.fh-pinkafeld.ac.at
> Tel.: 0043/3357/45370-1324
> Fax: 0043/3357/45370/1010
>
>
>                    Yahoo! Groups Sponsor
                        ADVERTISEMENT


>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/CBxunD/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/