Re: [EnergyPlus_Support] VAV system without reheat coils
Hello,
Here is the example that I have working for myself starting with the
example "VAVSingleDuctReheat.idf". For the Zone 1 VAV box
you can see what lines were changed to a null input and I commented
out the Reheat Coil. The 2nd zone remains with a Reheat Coil and
you should see the differences betrween the objects. Also make sure
that you have the new version 1.0.3 EnergyPlus executable which allows
for this scenario and does not produce the error message.
SINGLE DUCT:VAV:REHEAT,
Zone 1 VAV System, !- Name of System
FanAndCoilAvailSched, !- Availability schedule
for VAV System
Zone 1 Reheat Air Outlet Node, !- Damper Outlet
Node
Zone 1 Damper Inlet Node, !- Damper Inlet
Node
0.47, !- Maximum air flow rate {m3/s}
0.8, !- Min air flow
, !- Control node
, !- Reheat Component Object
, !- Name of Reheat Component
, !- Max Reheat Water Flow {m3/s}
, !- Min Reheat Water Flow {m3/s}
Zone 1 Reheat Air Outlet Node, !- Reheat Air
Outlet Node
; !- Convergence Tolerance
SINGLE DUCT:VAV:REHEAT,
Zone 2 VAV System, !- Name of System
FanAndCoilAvailSched, !- Availability schedule
for VAV System
Zone 2 Reheat Air Inlet Node, !- Damper Outlet
Node
Zone 2 Damper Inlet Node, !- Damper Inlet
Node
0.36, !- Maximum air flow rate {m3/s}
0.3, !- Min air flow
Zone 2 Reheat Water Inlet Node, !- Control
node
COIL:Water:SimpleHeating, !- Reheat Component
Object
Reheat Coil Zone 2, !- Name of Reheat
Component
0.0013, !- Max Reheat Water Flow {m3/s}
0.0, !- Min Reheat Water Flow {m3/s}
Zone 2 Reheat Air Outlet Node, !- Reheat Air
Outlet Node
0.001; !- Convergence Tolerance
! COIL:Water:SimpleHeating,
! Reheat Coil Zone 1, !- Coil Name
! FanAndCoilAvailSched, !- Available
Schedule
! 400.0, !- UA of the Coil {W/K}
! 0.0013, !- Max Water Flow Rate of Coil
{m3/s}
! Zone 1 Reheat Water Inlet Node, !-
Coil_Water_Inlet_Node
! Zone 1 Reheat Water Outlet Node, !-
Coil_Water_Outlet_Node
! Zone 1 Reheat Air Inlet Node, !-
Coil_Air_Inlet_Node
! Zone 1 Reheat Air Outlet Node; !-
Coil_Air_Outlet_Node
COIL:Water:SimpleHeating,
Reheat Coil Zone 2, !- Coil Name
FanAndCoilAvailSched, !- Available
Schedule
400.0, !- UA of the Coil {W/K}
0.0013, !- Max Water Flow Rate of Coil
{m3/s}
Zone 2 Reheat Water Inlet Node, !-
Coil_Water_Inlet_Node
Zone 2 Reheat Water Outlet Node, !-
Coil_Water_Outlet_Node
Zone 2 Reheat Air Inlet Node, !-
Coil_Air_Inlet_Node
Zone 2 Reheat Air Outlet Node; !-
Coil_Air_Outlet_Node
Thanks
Dr. Richard Liesen
Associate Director, Building Systems Laboratory
Department of Mechanical and Industrial Engineering
University of Illinois at Urbana-Champaign
www.bso.uiuc.edu
At 11:03 PM 12/5/2002, HSIEH Chun-Ming wrote:
Hello:
Thank you for adding the possibility to simulate a VAV system without
reheat coils.
I started from the example "VAVSingleDuctReheat.idf",
and left some fields to be blank according to the input-output reference
(P433-434).
But I got the severe messages as follows:
** Severe ** During Single Duct:VAV:Reheat Input,
Invalid Component
Type input=
** ~~~ ** Component name=
** ~~~ ** In Single
Duct:VAV:Reheat=ZONE 1 VAV SYSTEM
** Fatal ** Errors found in getting Sys
input
Do I forgot to do something else,
for example: to delect the Coil:Water:SimpleHeating, the branch of
heating system or something like that?
What I want is to simualte a VAV cooling system(only with cooling coil,
but without reheat and heating coil).
Is there any example?
Thank you very much.
Chunming
| Yahoo! Groups Sponsor |
ADVERTISEMENT
![]() |
|
![]() |
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.