Re: [EnergyPlus_Support] Ground Temperatures on weather file
The ground temperatures listed in the weather file are "undisturbed"
ground temperatures, like what you would see in the middle of an open
field. The ground underneath a building tends to be much closer to
the indoor temperature of the building than the undisturbed
temperatures.
There is a utility included with EnergyPlus called "slab.exe" in the
EnergyPlus\PreProcess\GrndTempCalc\ folder. This utility calculates
monthly core, perimeter, and average ground temperatures using a
description of the floor slab, the average indoor temperature, the
soil conditions, and the weather file for a given location. Docs for
it are in AuxiliaryPrograms.pdf, p. 38 (v1.0.3). Otherwise, 18C is a
reasonable value to use for most commercial applications in the U.S.
On 7 Jan 2003, at 11:38, Linda Lawrie wrote:
> At 11:10 AM 1/7/2003, TangoJim wrote:
>
> >There seems to be three sets of ground temperatures
> >listed on each of the weather files with five
> >parameters (?) used to generated these ground
> >temperatures.
> If you look at the stats file from a conversion, things are a little
> clearer:
>
> - Monthly Calculated "undisturbed" Ground Temperatures °C
> Jan Feb Mar Apr May Jun Jul
> Aug Sep Oct Nov Dec
> .5
> m 0.9 -0.1 2.0 6.7 12.9 18.8 22.8
> 24.0 21.8 17.0 10.8 5.0
> 2.0
> m 4.9 3.1 3.5 6.2 10.4 15.1 18.9
> 20.8 20.3 17.6 13.3 8.7
> 4.0
> m 8.2 6.3 5.9 7.0 9.5 12.7 15.6
> 17.6 18.0 16.8 14.3 11.1
>
> Sorry, it probably wraps. Even clearer is a CSV rendition:
>
> Number of Ground Temperature Depths,Ground Temperature Depth {m},Soil
> Conductivity {W/m-K},Soil Density {kg/m3},Soil Specific Heat
> {J/kg-K},Jan {C},Feb{C},Mar {C},Apr {C},May {C},Jun {C},Jul {C},Aug
> {C},Sep {C},Oct {C},Nov {C},Dec {C},<repeat to Number of temperature
> depths>
> 3,.5,,,,-22.93,-24.77,-21.07,-12.58,-1.53,9.08,16.38,18.41,14.56,5.92,
> -5.16,-15.69,2,,,,-15.84,-19.12,-18.31,-13.51,-5.90,2.44,9.27,12.78,11
> .91,6.98,-0.68,-9.01,4,,,,-9.93,-13.30,-14.07,-12.00,-7.54,-1.90,3.40,
> 6.97,7.74,5.56,1.05,-4.60
>
> Lacking a specified soil diffusivity for the particular location, the
> default is used:
>
> -- Ground temps produced with a standard soil diffusivity of
> 2.3225760E-03 {m**2/day}
>
> (Not the same location in both examples)
>
> The auxiliary programs document and descriptions of the Weather "IDD"
> format also describe each field that is listed on the EPW and CSV
> files. CSV file is easier to read as it also includes this
> information in the line preceding. The algorithm used is adapted from
> that used in the DOE-2 Weather Processor.
>
>
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Flexible Keyboard is the ideal accessory for
> PDA users that are on the move.
> http://us.click.yahoo.com/dCBVZC/WnCFAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Turn flat surfaces into speakers with the Soundbug.
http://us.click.yahoo.com/QWAVSC/onCFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/