[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Building of eight plans
Cristina:
In the ZONE object, the "Multiplier" field is used to replicate a
zone. In your case, you would enter 6 in this field for each of the
four dwellings in your intermediate floor description. This
multiplier is applied to the zone heating and cooling loads (and any
zone electric and gas use) before they are passed to the HVAC system.
If you are autosizing, the system sizes should be approximately 6
times larger. If you are not autosizing, then you need to specify
equipment sizes adequate to meet the multiplied load.
Mike
On 15 Jan 2003, at 17:15, Cristina Castaño/LABEIN wrote:
>
> Hi,
>
> We are interested in modeling the entire building. We have used the
> multipliers for the intermediate floors but the results are almost
> equals. Does Energy Plus understand that there are six intermediate
> floors?. We think that we have not understood how to use the
> multipliers, could you help us,please?.
>
> Best regards,
> Cristina
>
>