[EnergyPlus_Support] Re: Fans
> Yes, these two fan objects are quite similar.
>
> Fan:Simple:Const Volume models a constant air volume fan that runs
> continuously when it is scheduled "ON".
>
> FAN:SIMPLE:OnOff models a constant air volume fan that is available
to
> operate when it is scheduled "ON". However, it only operates when
the
> cooling or heating system comes on to meet a cooling or heating
load
for
> that simulation time step. The fan cycles on and off with the
cooling or
> heating system (i.e., AUTO fan mode). If you look at objects
"UNITARY
> SYSTEM:..", "FURNACE:..." and "AIR CONDITIONER:WINDOW:CYCLING", you
see the
> input field "Operating Mode" or "Operation Mode". If you choose
> "CycFanCycComp" or "CycFanCycCoil", then the FAN:SIMPLE:OnOff
object
needs
> to be specified to get the fan power and fan heat correctly
calculated. If
> you choose "ContFanCycComp" or "ContFanCycCoil", then you should
specify
> Fan:Simple:Const Volume (although the on/off fan object would
probably work
> in this case too).
I need to clarify my earlier response. The description about when to
use Fan:Simple:Const Volume and when to use Fan:Simple:OnOff for the
object "AIR CONDITIONER:WINDOW:CYCLING" is correct.
Currently, Fan:Simple:OnOff is the only valid supply air fan for use
with the objects "UNITARY SYSTEM:..." and "FURNACE:...". Just make
sure that the part-load fraction correlation (function of part load
ratio) for the heating and/or cooling coils is input correctly as
described in the IO Reference Manual (i.e., the curve should be
normalized to 1.0 when the part-load ratio equals 1.0). If you've
input the part-load fraction correlation correctly, then
Fan:Simple:OnOff will work for both continuous fan operation
(ContFanCycCoil) as well as OnOff operation (CycFanCycCoil).
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/