Franz:
What type of system are you modeling? Is this a single-zone air
handler or does it serve multiple zones? If it is a single-zone air
handler, then use the furnace or unitary equipment to control heating
and cooling to meet the zone's needs. If it is a multi-zone air
handler, then you can use setpoint managers to deactivate equipment
based on the zone with the greatest needs (set point manager:warmest)
or reset control temeperatures based on outdoor air temperature (set
point manager:outside air).
Mike
On 11 Feb 2003, at 11:51, Franz Muller wrote:
> Dear E+ users,
>
> I am trying to model HVAC consisting of a heater, humidifier, cooler,
> preheater and van. During the simulation all 5 elements are trying to
> reach the desired room conditions. That is sometimes not useful as
> they are working simultaneously and I get a huge energy consumption.
> During winter time I want to bypass the cooler and during summer time
> I want to bypass the preheater as I do not need them at this time. One
> possibilty is to define availability schedules for each element,
> turning off the heater in summer time for example. But I want to have
> them in operation by defining a temperature band, eg. the cooler
> should only be active at temperatures from 20 to 40 °C. I could define
> of course a schedule after running a simulation and looking at the
> temperatures there. But that is not that I want. Is it possible to
> make the components working by connecting them to a temperature
> sensor. Or the other way round can I generate a availabilty schedule
> for the components by a definition of IF THEN concerning temperatures.
> This is important for me if I change the location for example from
> Moscow to Sao Paulo as the weather files are quite different and it
> would take a lot of time to generate all the schedules for the new
> location.
>
> I hope I could make my problem clear.
> Thanks for your help in advance.
>
> Franz
>
> --
> +++ GMX - Mail, Messaging & more http://www.gmx.net +++
> NEU: Mit GMX ins Internet. Rund um die Uhr für 1 ct/ Min. surfen!
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/