Re: [EnergyPlus_Support] Re: help



For item 4 "Filtration/ Air Cleaning to reduce OA requirements as 
allowed by Standard 62 5. Run Around Loop 6. Underfloor air 
distribution", there is no automatic adjustment.  You would need to 
determine the allowed reduction and specify different OA flow rates.

For item 6 "Underfloor air distribution", it is possible to 
approximate this using the current supply plenum model, but 
EnergyPlus zones are currently well-mixed, so you cannot model the 
stratification effects.  Work is underway for a 2-node stratification 
model, but I do not know the target completion date.  One other 
consideration with current capabilities is the rejection of equipment 
heat into the return air.  The EnergyPlus LIGHTS object has this 
capability and could be used as a proxy for other electric equipment 
by setting the fraction visible to zero.

Mike




On 10 Feb 2003, at 22:55, don_shirey shirey@xxxxxxxxxxxxxxxxxx wrote:

> 3. Desiccant Wheel can already be modeled (object = DESICCANT 
> DEHUMIDIFIER:SOLID) 
> 
> A model for an enthalpy recovery wheel (latent + sensible) should be
> included in the next release (Version 1.1). 
> 
> A model for CO2-based demand ventilation is coming later this year. 
> In the meantime, you can simply schedule the outdoor ventilation air
> using the same schedule you use for occupancy.  This will at least
> give you a first-order approximation. 
> 
> Please clarify what you mean by runaround loops:  sensible heat 
> recovery from exhaust air to preheat incoming ventilation air,
> or air-to-air heat exchanger used to improve the dehumidification
> performance of a cooling coil. 
> 
> I'm not sure about the status of the other areas. 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "liu simeng" 
> <simon0176@h...> wrote:
> > 
> > Can anyone tell me which one can be modeled in E+ in the following 
> list:
> > 
> > 1. CO2-based demand ventilation
> > 2. Latent Heat Wheel
> > 3. Dessicant Wheel
> > 4. Filtration/ Air Cleaning to reduce OA requirements as allowed by
> > Standard 62 5. Run Around Loop 6. Underfloor air distribution
> > 
> > Thank you for your help!
> > 
> > Best regards,
> > 
> > Simeng Liu
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/