Re: [EnergyPlus_Support] DX Coil in Airloop (was New file uploaded . . .)
Isidor:
Coil:DX:CoolingBypassFactorEmpirical cannot be used directly in an
airloop, it must be part of one of the following components:
DXSystem:AirLoop, UNITARYSYSTEM:HEATPUMP:AIRTOAIR,
UNITARYSYSTEM:BLOWTHRU:HEATCOOL, FURNACE:BLOWTHRU:HEATCOOL, or AIR
CONDITIONER:WINDOW:CYCLING (the last one is zone equipment, not for
air loops).
Use DXSystem:AirLoop is you will control the leaving temperature of
the DX coil to a specified setpoint. Use
UNITARYSYSTEM:BLOWTHRU:HEATCOOL or FURNACE:BLOWTHRU:HEATCOOL if the
DX coil is controlled to meet the load in a specified zone.
Mike
On 12 Feb 2003, at 15:49, Isidor Giglmayr wrote:
> ** High Priority **
>
> Dear Linda,
>
> thanks for uploading the new IDD-file such quick. Now the proplem with
> the curves is solved. Meanwhile I used the Wordpad to fill in the
> missing line into my idf-File. But why can't I use
> Coil:DX:CoolingBypassFactorEmpirical in my AirLoop? I get following
> error: Severe ** Invalid Air Loop Component
> Type=COIL:DX:COOLINGBYPASSFACTOREMPIRICAL** Is that component not
> useful for cooling the air in a primary loop? Which component do you
> suggest?
>
> Kind regards
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/