Re: [EnergyPlus_Support] Maximum iterations exceeded for all HVAC loops
Some further advice on checking node connections:
In the *.bnd output file, there is a list of all node names used in
your input file. After each node name is a count of how many times
it was referenced after it was created. Nodes with a zero reference
count as suspect and may indicate an error. Exceptions where a zero
is expected are: zone air nodes and condenser inlet nodes for an air
cooled chiller. There may be other exceptions which I have not
thought of.
Mike
On 12 Feb 2003, at 10:39, Michael J. Witte wrote:
> James:
>
> This usually indicates a bad configuration that is impossible to
> solve. It is probably an incorrect node name somewhere in your
> system. Many node connections are checked for validity, but many are
> not. Review your node names to make sure that a complete loop is
> defined and there are no dangling nodes. Also check for controllers
> that may be operating without a valid setpoint node.
>
> Mike
>
>
> On 12 Feb 2003, at 11:55, James O'Donnell wrote:
>
> > Dear All,
> > Could anybody please explain or offer possibe reasons to why
> > my
> > simple model consisting of a fan a heating coil and a cooling coil
> > would produce the following warnings?
> >
> >
> > ************* Testing Individual Branch Integrity
> > ************* All Branches passed integrity testing
> > ************* No node connection errors were found.
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 00:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 01:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 02:10
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops,
> > SUMMER DESIGN DAY, 07/21 02:10
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 50
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 100
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 150
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 200
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 250
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 300
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 350
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 400
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 450
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 500
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 550
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 600
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 650
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 700
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 750
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 800
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 850
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 900
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 950
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1000
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1050
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1100
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1150
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1200
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1250
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1300
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1350
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1400
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1450
> > ** Warning ** SimHVAC: Exceeding max iterations continues... 1500
> > ************* EnergyPlus Completed Successfully-- 44 Warning; 0
> > Severe
> > Errors; Elapsed Time=00hr 00min 29sec
> >
> >
> > Yours Thankfully:
> > James
> > O'Donnell
> >
> >
> > ------------------------ Yahoo! Groups Sponsor
> > ---------------------~--> Get 128 Bit SSL Encryption!
> > http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
> > --------------------------------------------------------------------
> > -~ ->
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to
> > http://docs.yahoo.com/info/terms/
> >
>
>
>
> ========================================================
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/