Re: [EnergyPlus_Support] ground-coupled heat transfer
Regarding ground-coupled heat transfer:
In the Auxiliary Programs document, there is a section on Ground Heat
Transfer which describes how to use the ground temperature
preprocessor which is provided with EnergyPlus. It is recommended
that you do not add any soil or ficititious layers to your slab or
basement wall constructions. Use the ground temperature preprocessor
to determine the monthly ground temperatures which are the
temperatures at the outside face of ground-coupled surfaces.
Do not use the "ground temperatures" which are listed in the weather
files, because these are thermally undisturbed ground temperatures
that one would find in an open field. The temperatures beneath a
conditioned building are quite different.
Mike Witte
On 18 Mar 2003, at 21:40, zhaicq98 wrote:
> Hi,
>
> I am wondering if the simulation of basement and slab-on-ground floor
> in EnergyPlus is the same as that in DOE2. Do I need to add soil and
> fictitious insulation layer to the below grade wall and slab-on-
> ground floor construction in EnergyPlus simulation as what is done in
> DOE2?
>
> Another problem I encountered is when I tried to simulate a glass
> curtain wall, I got an error message which said sunlit area too large.
> I had a wall which was 14m high, and I made a large window (13.8m
> high) on it. I tried to make the window a little smaller (12.5m high)
> and I also tried to split the large window into three small ones, but
> in both cases I still got this error message.
>
> Can anyone give me some hints on these two questions?
>
> Thank you,
> Chaoqin
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/