Hi Chunming:

I am trying to find out if this limit can be increased.  If not, you 
are limited to 10 plenums per air primary loop.  You cannot use more 
than one return air path in an air loop, so you would need to use 2 
air primary loops in your building.  We do not have any examples of 
this.  You need to repeat the air primary loop and all of its 
subcomponents (branch list, main branch, coils, fan, supply air path, 
return air path, controllers, etc.).  Your chilled water/hot water 
supply loops can serve both air loops.

Mike

On 22 Apr 2003, at 23:14, HSIEH Chun-Ming wrote:

> Hello,
> 
> I am chunming. I have a question about zone return air path.
> In each of the "ZONE RETURN AIR PATH",  there is a limitation that at
> most 10 component can be input. But now, I am simulating a building
> with 15F, each story with a plenum on it. That means 15 plenums here.
> Do I need to create the other new zone return air path or even a air
> primary loop in this case? Is there any example with mutiple air paths
> or air primary loop in E+? Thank you very much.
> 
> Chunming
> 
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/xaxhjB/hdqFAA/VygGAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/W7NydA/hdqFAA/bW3JAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/