[EnergyPlus_Support] Window Calculation
Dear E+ User
1) In the case of windows, the external film coefficient cannot be
set with the object ?ConvectionCoefficients?. This means, if a value is
defined, the output variable for the window external convection
coefficient is zero. Is this deliberate?
2) As defined on page 41 in the Output Details and Examples-
manual, the calculated conductance does not include film coefficients.
Comparing this result to the Window5 calculation, values are the same,
but the Window5 calculation includes film coefficients. Might it be
possible, that the E+ output for the U-Value includes the film
coefficient? In that case, can the window U-Value be assumed to be
constant, independent of the variable external convection coefficient?
I would appreciate your comments.
Alexander
_______________________________________
DI (FH) Alexander Beisteiner
Wissenschaftlicher Mitarbeiter
Forschungs- und Technologietransfer Pinkafeld GmbH
Steinamangerstraße 21
A - 7423 Pinkafeld
Tel.: +43-3357-45370 DW 1324
Fax.: +433357-45370 DW 1010
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/bW3JAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/