Some email has gone on behind the scenes, but the answers are included below:
At 02:32 AM 4/29/2003, Alexander Beisteiner wrote:
>1) In the case of windows, the external film coefficient cannot be
>set with the object "ConvectionCoefficients". This means, if a value is
>defined, the output variable for the window external convection
>coefficient is zero. Is this deliberate?
This was a bug in the program. It is not (1.1.0.018) doing the user
supplied convection coefficients (an advanced feature) correctly. We hope
to issue an update for this and several other problems that were
late-breaking soon.
>2) As defined on page 41 in the Output Details and Examples-
>manual, the calculated conductance does not include film coefficients.
>Comparing this result to the Window5 calculation, values are the same,
>but the Window5 calculation includes film coefficients. Might it be
>possible, that the E+ output for the U-Value includes the film
>coefficient? In that case, can the window U-Value be assumed to be
>constant, independent of the variable external convection coefficient?
>
The documentation was incorrect -- windows are reported WITH film
coefficients. However, there is a change request (CR) to have both Window
Constructions and other Constructions reported with and without film
coefficients in this report. (As noted above, the other Constructions are
already reported WITHOUT film coefficients). However, note that user
supplied convection coefficients add a new degree of complexity here --
therefore, the nominal film coefficient reporting will be for standard
conditions -- and will be documented thereof.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/bW3JAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/