Fred Winkelmann

no_rb wrote:

> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Frederick Winkelmann
> <FCWinkelmann@l...> wrote:
> > Only the daylight illuminance can be output. However, if the
> overhead electric lights are on, you can calculate the total
> > illuminance as follows:
> >
> > If daylight illuminance <= illuminance set point, total illuminance
> = illuminance set point.
> >
>
> so, I guess the assumption is that the (setpoint illuminance -
> daylight illuminance) comes from the electrical lighting no matter
> what the design wattage of the electrical lighting and that the max
> wattage of the electrical lighting corresponds to the setpoint
> illuminance. Is that correct?
>
> Thanks
>
> Rohini
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs from home.
Over 14,500 titles. Free Shipping
& No Late Fees. Try Netflix for FREE!
http://us.click.yahoo.com/BVVfoB/hP.FAA/uetFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/