Brent:
When active, DST will shift all scheduled items by one hour.
Reporting is always in standard time. I ran a quick experiment with
the PurchAir example file. I added the DST object and ran from April
15 to May 15. What I found is that the DST is not active unless the
RUN PERIOD field for DST says "Yes".
RunPeriod,
4, !- Begin Month
15, !- Begin Day Of Month
5, !- End Month
15, !- End Day Of Month
UseWeatherFile, !- Day Of Week For Start Day
Yes, !- Use WeatherFile Holidays/Special Days
Yes, !- Use WeatherFile DaylightSavingPeriod <-- MUST BE YES
No, !- Apply Weekend Holiday Rule
Yes, !- Use WeatherFile Rain Indicators
Yes; !- Use WeatherFile Snow Indicators
Mike
On 6 May 2003, at 15:21, Griffith, Brent wrote:
>
> Does anyone know what actually happens when Daylight Savings Time is
> turned "on" in EnergyPlus? A simple test comparing annual runs with
> and without DST showed no difference in the hourly results. I used
> normal EnergyPlus weather files and the object "DaylightSavingPeriod,
> 1st Sunday in April, Last Sunday in October;" Do the output time
> stamps shift with DST or do they stay in Standard time? What happens
> to those messy hours at the point of change?
>
> Brent
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Make Money Online Auctions! Make $500.00 or
> We Will Give You Thirty Dollars for Trying!
> http://us.click.yahoo.com/KXUxcA/fNtFAA/uetFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading!
Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/cjB9SD/od7FAA/uetFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/