Re: [EnergyPlus_Support] Cooling & Heating Design Air Flow Method
If you specify a volumetric airflow rate in the zone sizing object,
then this overrides the design load calculation for that zone. The
specified rate is then used when sizing the central air handling
components (fan, coil, etc.) This does not override the specified
supply air temperature for sizing. Supply air volumes are sized to
meet the sensible load in the zone based on the design day
simulations. For hourly details of these loads, see the *.zsz and
*.ssz output files.
Mike
On 7 May 2003, at 14:32, Ruchi Choudhary wrote:
>
> Dear All,
>
> In the Zone Sizing Object there are two fields that allow the user to
> either specify the volumetric airflow rate, or compute it on the basis
> of the design day simulation.
>
> My understanding is that the mass flow rates computed by the zone
> sizing object are used in conjunction with the system supply
> temperature and outside air flow rate to compute the system capacity.
>
> So if I specify the volumetric airflow rate for a zone, will it be
> used to determine the system capacity rather than the output from
> design day simulation? By doing so, I am implicitly also over-riding
> the design load computed by the zone-sizing object and zone supply air
> temperature specification?
>
> Also, the *.eio file lists the design volumetric air flow rates for
> each zone. I am assuming these are computed on the basis of the design
> load and zone-sizing specs. (supply temperature and humidity)?
>
> ruchi.
>
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Rent DVDs Online - Over 14,500 titles. No
> Late Fees & Free Shipping. Try Netflix for FREE!
> http://us.click.yahoo.com/YoVfrB/XP.FAA/uetFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs from home.
Over 14,500 titles. Free Shipping
& No Late Fees. Try Netflix for FREE!
http://us.click.yahoo.com/BVVfoB/hP.FAA/uetFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/