Re: [EnergyPlus_Support] freezer cells
Roberto:
EnergyPlus does not have the capability to fully model refrigerated 
cases and walk-in freezers, because it does not have any way to model 
the frost loads.  If the refrigeration energy use is important for 
your model, you should be able to get a "chilled water" loop to go 
cold enough to cool these spaces.  You will need to make sure that 
all of the setpoints in your system are low enough, especially the 
chilled water loop setpoint and minimum temperature.  And you will 
need to make some allowance for the missing frost/defrost loads.  
If the refrigeration energy use is not important, but you just want 
to see the impact of the cold spaces on the occupied spaces, then you 
could use purchased air to hold the cold spaces at the desired 
temperature.
Mike
On 28 May 2003, at 9:33, Roberto Lollini wrote:
> I'm analysing a big shopping centre with complicated (for me) HVAC
> plants. The centre is made up of several thermal zones: retail,
> offices, workings (bakery, butcher's shop, ...) and freezers
> completely inside the shopping centre envelope. There are two types of
> freezer: Normel Temperature (0-4 °C) and Low Temperature (-20 °C). I'm
> trying to simulate the performances of low temperature (-20 °C) cells
> (volume about 80 m3), but without any results, because the ambient
> temperature doesn't want to reach the set-point. I tried to use
> several kind of plants (const cop chiller with simple cooling coil and
> single duct noreheat former) also modifing the setting of the proposed
> examples, but without meet success. Is it possible in Energy+ to
> analyse this very cold kind of zone? Could anyone help me?
> 
> Sorry for my bad English and for my confused explanation ...
> Thank you very much for your attention,
> Roberto
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get A Free Psychic Reading! Your Online
> Answer To Life's Important Questions.
> http://us.click.yahoo.com/Lj3uPC/Me7FAA/CNxFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 
========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/CNxFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
 
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/