[EnergyPlus_Support] Re: IFC>IDF problems
Here is how I created my IFC(2x) from ADT3.3 with GtsIfc2xUtility:
1a. Open 1zoneUncontrolled.dxf in ADT3.3
1b. change unit to decimal.
2a. add 1 space, COMMAND:space>Add
2b. modify space properties(adjust ceiling and floor thickness)
3. add 4 walls, COMMAND:wall>Add
4a. add 1 roof, COMMAND:roof>Add
4b. modify roof thickness.
5. add 1 floor, COMMAND:slab>Add
6. save dwg
7. export IFC using cascade menu GtsIfc2xUtility>Export IFC 2x...
=========
The following is the IFC file.
(A copy uploaded to Files[1zonetest] folder)
the error message when run this IFC with IFCtoIDF is:
---
The instruction at "0x10003658" referenced memory at "0x00000004".
The memory could not be "read".
Click on OK to terminate the program
Click on CANCEL to debug the program
---
the debuging window shows:
Unhandled exception in IFCtoIDF.exe(EPLUSBSCLIENT.DLL): 0xC000005:
Access Violation
=====1zonetestIFC2x.ifc==========
ISO-10303-21;
HEADER;
FILE_DESCRIPTION(('IFC 2x'),'2;1');
FILE_NAME('C:\\Eplus1_1\\ExampleFiles\\1zonetestIFC2x.dwg','2003-05-
28T23:55:58',('Anyone'),('Autodesk'),'GtsIfc2xUtility Version: 2, 0,
0, 7 - IFC Toolbox Version 2.x (00/11/07)','AutoCAD','AutoCAD');
FILE_SCHEMA(('IFC2X_FINAL'));
ENDSEC;
DATA;
#1=IFCSIUNIT(*,.TIMEUNIT.,$,.SECOND.);
#2=IFCSIUNIT(*,.MASSUNIT.,$,.GRAM.);
#3=IFCDIMENSIONALEXPONENTS(1,0,0,0,0,0,0);
#4=IFCSIUNIT(*,.LENGTHUNIT.,$,.METRE.);
#5=IFCMEASUREWITHUNIT(IFCRATIOMEASURE(0.0254),#4);
#6=IFCCONVERSIONBASEDUNIT(#3,.LENGTHUNIT.,'Inch',#5);
#7=IFCSIUNIT(*,.AREAUNIT.,$,.SQUARE_METRE.);
#8=IFCSIUNIT(*,.VOLUMEUNIT.,$,.CUBIC_METRE.);
#9=IFCUNITASSIGNMENT((#6,#7,#8,#1,#2));
#10=IFCCARTESIANPOINT((0.,0.,0.));
#11=IFCDIRECTION((0.,0.,1.));
#12=IFCDIRECTION((1.,0.,0.));
#13=IFCAXIS2PLACEMENT3D(#10,#11,#12);
#14=IFCGEOMETRICREPRESENTATIONCONTEXT
('TestGeometricContext','TestGeometry',3,0.,#13,$);
#15=IFCPERSON('','Anyone','Anyone',$,$,$,$,$);
#16=IFCORGANIZATION('','Autodesk','',$,$);
#17=IFCPERSONANDORGANIZATION(#15,#16,$);
#18=IFCAPPLICATION(#16,'GtsIfc2xUtility Version: 2, 0, 0,
7','GtsIfc2xUtility for ADT3.3','Autodesk Architectural Desktop');
#19=IFCOWNERHISTORY(#17,#18,$,.ADDED.,0,$,$,1054184158);
#20=IFCPROJECT
('34US8ti5HC6hjf3ZRR9mCM',#19,'1zonetestIFC2x','Ifc2xImport #0',$,$,$,
(#14),#9);
#27=IFCCARTESIANPOINT((4.440892098500626E-016,-1.776356839400251E-
015,0.));
#28=IFCDIRECTION((0.,0.,1.));
#29=IFCDIRECTION((1.,8.15911934107727E-016,0.));
#30=IFCAXIS2PLACEMENT3D(#27,#28,#29);
#31=IFCLOCALPLACEMENT(#25,#30);
#35=IFCLINE(#32,#34);
#32=IFCCARTESIANPOINT((-3.552713678800501E-015,0.));
#34=IFCVECTOR(#33,15.24);
#33=IFCDIRECTION((1.,0.));
#36=IFCCARTESIANPOINT((-3.552713678800501E-015,0.));
#37=IFCCARTESIANPOINT((15.24,0.));
#38=IFCTRIMMEDCURVE(#35,(IFCPARAMETERVALUE(0.),#36),(IFCPARAMETERVALUE
(1.),#37),.T.,.CARTESIAN.);
#39=IFCSHAPEREPRESENTATION(#14,'Axis','GeometricSet',(#38));
#41=IFCCARTESIANPOINT((0.09999999999999962,0.1));
#42=IFCCARTESIANPOINT((-0.1000000000000005,-0.1));
#43=IFCCARTESIANPOINT((15.34026350415452,-0.1));
#44=IFCCARTESIANPOINT((15.13973649584547,0.1));
#45=IFCCARTESIANPOINT((0.09999999999999962,0.1));
#46=IFCPOLYLINE((#41,#42,#43,#44,#45));
#47=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#46);
#48=IFCCARTESIANPOINT((0.,0.,0.));
#49=IFCDIRECTION((0.,0.,1.));
#50=IFCDIRECTION((1.,0.,0.));
#51=IFCAXIS2PLACEMENT3D(#48,#49,#50);
#52=IFCDIRECTION((0.,0.,1.));
#53=IFCEXTRUDEDAREASOLID(#47,#51,#52,4.6);
#55=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#53));
#40=IFCPRODUCTDEFINITIONSHAPE($,$,(#39,#55));
#56=IFCWALLSTANDARDCASE
('3OAlPI2Zz7Phxo_QYijFer',#19,$,'',$,#31,#40,$);
#57=IFCMATERIAL('Unnamed');
#58=IFCMATERIALLAYER(#57,0.2,.F.);
#59=IFCMATERIALLAYERSET((#58),'Standard');
#60=IFCMATERIALLAYERSETUSAGE(#59,.AXIS2.,.POSITIVE.,-0.1);
#61=IFCRELASSOCIATESMATERIAL('3cNUASiEv2V8drkHqdgX4s',#19,$,$,
(#56),#60);
#62=IFCCARTESIANPOINT((15.24,1.065814103640151E-014,0.));
#63=IFCDIRECTION((0.,0.,1.));
#64=IFCDIRECTION((-0.002631569835301389,0.9999965374141063,0.));
#65=IFCAXIS2PLACEMENT3D(#62,#63,#64);
#66=IFCLOCALPLACEMENT(#25,#65);
#70=IFCLINE(#67,#69);
#67=IFCCARTESIANPOINT((0.,0.));
#69=IFCVECTOR(#68,15.20005263148784);
#68=IFCDIRECTION((0.9999999999999999,0.));
#71=IFCCARTESIANPOINT((0.,0.));
#72=IFCCARTESIANPOINT((15.20005263148784,0.));
#73=IFCTRIMMEDCURVE(#70,(IFCPARAMETERVALUE(0.),#71),(IFCPARAMETERVALUE
(1.),#72),.T.,.CARTESIAN.);
#74=IFCSHAPEREPRESENTATION(#14,'Axis','GeometricSet',(#73));
#76=IFCCARTESIANPOINT((0.1002635041545252,0.09999999999999609));
#77=IFCCARTESIANPOINT((-0.1002635041545253,-0.09999999999999965));
#78=IFCCARTESIANPOINT((15.29952769710464,-0.1000000000000032));
#79=IFCCARTESIANPOINT((15.10057756587105,0.09999999999999609));
#80=IFCCARTESIANPOINT((0.1002635041545252,0.09999999999999609));
#81=IFCPOLYLINE((#76,#77,#78,#79,#80));
#82=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#81);
#83=IFCCARTESIANPOINT((0.,0.,0.));
#84=IFCDIRECTION((0.,0.,1.));
#85=IFCDIRECTION((1.,0.,0.));
#86=IFCAXIS2PLACEMENT3D(#83,#84,#85);
#87=IFCDIRECTION((0.,0.,1.));
#88=IFCEXTRUDEDAREASOLID(#82,#86,#87,4.6);
#90=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#88));
#75=IFCPRODUCTDEFINITIONSHAPE($,$,(#74,#90));
#91=IFCWALLSTANDARDCASE
('1w2v__2Mr5xPQINaeY_2QF',#19,$,'',$,#66,#75,$);
#92=IFCRELASSOCIATESMATERIAL('2zO8ZnuEX5u8RjGYhqaI3c',#19,$,$,
(#91),#60);
#93=IFCRELCONNECTSPATHELEMENTS
('2ijPTSPAT3yB2N$k7jHB0J',#19,$,$,$,#91,#56,(1),
(1),.ATEND.,.ATSTART.);
#94=IFCCARTESIANPOINT((15.19999999999998,15.20000000000003,0.));
#95=IFCDIRECTION((0.,0.,1.));
#96=IFCDIRECTION((-0.9999965374141061,0.002631569835298824,0.));
#97=IFCAXIS2PLACEMENT3D(#94,#95,#96);
#98=IFCLOCALPLACEMENT(#25,#97);
#102=IFCLINE(#99,#101);
#99=IFCCARTESIANPOINT((0.,0.));
#101=IFCVECTOR(#100,15.20005263148781);
#100=IFCDIRECTION((1.,0.));
#103=IFCCARTESIANPOINT((0.,0.));
#104=IFCCARTESIANPOINT((15.20005263148781,0.));
#105=IFCTRIMMEDCURVE(#102,(IFCPARAMETERVALUE(0.),#103),
(IFCPARAMETERVALUE(1.),#104),.T.,.CARTESIAN.);
#106=IFCSHAPEREPRESENTATION(#14,'Axis','GeometricSet',(#105));
#108=IFCCARTESIANPOINT((0.09947506561679731,0.09999999999999609));
#109=IFCCARTESIANPOINT((-0.09947506561679731,-0.1000000000000032));
#110=IFCCARTESIANPOINT((15.30031613564233,-0.09999999999999965));
#111=IFCCARTESIANPOINT((15.09978912733328,0.09999999999999609));
#112=IFCCARTESIANPOINT((0.09947506561679731,0.09999999999999609));
#113=IFCPOLYLINE((#108,#109,#110,#111,#112));
#114=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#113);
#115=IFCCARTESIANPOINT((0.,0.,0.));
#116=IFCDIRECTION((0.,0.,1.));
#117=IFCDIRECTION((1.,0.,0.));
#118=IFCAXIS2PLACEMENT3D(#115,#116,#117);
#119=IFCDIRECTION((0.,0.,1.));
#120=IFCEXTRUDEDAREASOLID(#114,#118,#119,4.6);
#122=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#120));
#107=IFCPRODUCTDEFINITIONSHAPE($,$,(#106,#122));
#123=IFCWALLSTANDARDCASE('3ZAt7
$5057N9J3vspzkg7W',#19,$,'',$,#98,#107,$);
#124=IFCRELASSOCIATESMATERIAL('0Gy5FSPmL0Cxd$gZ2dVmSw',#19,$,$,
(#123),#60);
#125=IFCRELCONNECTSPATHELEMENTS
('3wLc5Jqq19GOIBJlNnmTOi',#19,$,$,$,#123,#91,(1),
(1),.ATEND.,.ATSTART.);
#126=IFCCARTESIANPOINT((-1.554312234475219E-
015,15.24000000000001,0.));
#127=IFCDIRECTION((0.,0.,1.));
#128=IFCDIRECTION((1.019889917634658E-016,-1.,0.));
#129=IFCAXIS2PLACEMENT3D(#126,#127,#128);
#130=IFCLOCALPLACEMENT(#25,#129);
#134=IFCLINE(#131,#133);
#131=IFCCARTESIANPOINT((0.,0.));
#133=IFCVECTOR(#132,15.24000000000001);
#132=IFCDIRECTION((1.,0.));
#135=IFCCARTESIANPOINT((0.,0.));
#136=IFCCARTESIANPOINT((15.24000000000001,0.));
#137=IFCTRIMMEDCURVE(#134,(IFCPARAMETERVALUE(0.),#135),
(IFCPARAMETERVALUE(1.),#136),.T.,.CARTESIAN.);
#138=IFCSHAPEREPRESENTATION(#14,'Axis','GeometricSet',(#137));
#140=IFCCARTESIANPOINT((0.1002635041545243,0.1));
#141=IFCCARTESIANPOINT((-0.1002635041545243,-0.1));
#142=IFCCARTESIANPOINT((15.34000000000001,-0.1));
#143=IFCCARTESIANPOINT((15.14000000000001,0.1));
#144=IFCCARTESIANPOINT((0.1002635041545243,0.1));
#145=IFCPOLYLINE((#140,#141,#142,#143,#144));
#146=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#145);
#147=IFCCARTESIANPOINT((0.,0.,0.));
#148=IFCDIRECTION((0.,0.,1.));
#149=IFCDIRECTION((1.,0.,0.));
#150=IFCAXIS2PLACEMENT3D(#147,#148,#149);
#151=IFCDIRECTION((0.,0.,1.));
#152=IFCEXTRUDEDAREASOLID(#146,#150,#151,4.6);
#154=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#152));
#139=IFCPRODUCTDEFINITIONSHAPE($,$,(#138,#154));
#155=IFCWALLSTANDARDCASE
('3CbhsDQoH79vW$OO9NQ4GN',#19,$,'',$,#130,#139,$);
#156=IFCRELASSOCIATESMATERIAL('0WZk9kkoPDoh7s8zHCxGAW',#19,$,$,
(#155),#60);
#157=IFCRELCONNECTSPATHELEMENTS
('2mxiRdqnbACwVE06x8EnJS',#19,$,$,$,#155,#123,(1),
(1),.ATEND.,.ATSTART.);
#158=IFCRELCONNECTSPATHELEMENTS
('3gKJq8cxn4IQ1BPTA_CHUO',#19,$,$,$,#155,#56,(1),
(1),.ATSTART.,.ATEND.);
#159=IFCCARTESIANPOINT((0.,0.,0.));
#160=IFCDIRECTION((0.,0.,1.));
#161=IFCDIRECTION((1.,0.,0.));
#162=IFCAXIS2PLACEMENT3D(#159,#160,#161);
#163=IFCLOCALPLACEMENT(#25,#162);
#164=IFCCARTESIANPOINT((0.,15.24,4.8));
#165=IFCCARTESIANPOINT((15.24,15.24,4.8));
#166=IFCCARTESIANPOINT((15.24,0.,4.8));
#167=IFCCARTESIANPOINT((0.,0.,4.8));
#168=IFCCARTESIANPOINT((0.,15.24,4.6));
#169=IFCCARTESIANPOINT((15.24,15.24,4.6));
#170=IFCCARTESIANPOINT((15.24,0.,4.6));
#171=IFCCARTESIANPOINT((0.,0.,4.6));
#172=IFCPOLYLOOP((#164,#167,#166,#165));
#173=IFCFACEOUTERBOUND(#172,.T.);
#174=IFCFACE((#173));
#175=IFCPOLYLOOP((#171,#168,#169,#170));
#176=IFCFACEOUTERBOUND(#175,.T.);
#177=IFCFACE((#176));
#178=IFCPOLYLOOP((#167,#164,#168,#171));
#179=IFCFACEOUTERBOUND(#178,.T.);
#180=IFCFACE((#179));
#181=IFCPOLYLOOP((#164,#165,#169,#168));
#182=IFCFACEOUTERBOUND(#181,.T.);
#183=IFCFACE((#182));
#184=IFCPOLYLOOP((#165,#166,#170,#169));
#185=IFCFACEOUTERBOUND(#184,.T.);
#186=IFCFACE((#185));
#187=IFCPOLYLOOP((#166,#167,#171,#170));
#188=IFCFACEOUTERBOUND(#187,.T.);
#189=IFCFACE((#188));
#190=IFCCLOSEDSHELL((#174,#177,#180,#183,#186,#189));
#191=IFCFACETEDBREP(#190);
#192=IFCSHAPEREPRESENTATION(#14,'Body','Brep',(#191));
#193=IFCPRODUCTDEFINITIONSHAPE($,$,(#192));
#194=IFCROOF
('0GBhRu7tDFw9Xl7zDO20do',#19,$,'',$,#163,#193,$,.FREEFORM.);
#195=IFCCARTESIANPOINT((4.440892098500626E-016,-1.776356839400251E-
015,-0.2));
#196=IFCDIRECTION((0.,0.,0.9999999999999999));
#197=IFCDIRECTION((1.,8.15911934107727E-016,0.));
#198=IFCAXIS2PLACEMENT3D(#195,#196,#197);
#199=IFCLOCALPLACEMENT(#25,#198);
#200=IFCCARTESIANPOINT((0.,0.));
#201=IFCCARTESIANPOINT((15.24,-2.761013168273541E-030));
#202=IFCCARTESIANPOINT((15.24000000000001,15.23999999999999));
#203=IFCCARTESIANPOINT((1.043609643147648E-014,15.24000000000001));
#204=IFCCARTESIANPOINT((0.,0.));
#205=IFCPOLYLINE((#200,#201,#202,#203,#204));
#206=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#205);
#207=IFCCARTESIANPOINT((0.,0.,0.));
#208=IFCDIRECTION((0.,0.,1.));
#209=IFCDIRECTION((1.,0.,0.));
#210=IFCAXIS2PLACEMENT3D(#207,#208,#209);
#211=IFCDIRECTION((0.,0.,1.));
#212=IFCEXTRUDEDAREASOLID(#206,#210,#211,0.2);
#214=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#212));
#215=IFCPRODUCTDEFINITIONSHAPE($,$,(#214));
#216=IFCSLAB('0IG$bYM8D7mgb6mx$ArPdO',#19,$,'',$,#199,#215,$,.FLOOR.);
#26=IFCBUILDING
('1tSI2uRPTBowmGn7GekJY6',#19,'1zonetestIFC2x','Ifc2xImport
#0',$,#25,$,'',.ELEMENT.,$,$,$);
#25=IFCLOCALPLACEMENT($,#24);
#24=IFCAXIS2PLACEMENT3D(#21,#22,#23);
#21=IFCCARTESIANPOINT((0.,0.,0.));
#22=IFCDIRECTION((0.,0.,1.));
#23=IFCDIRECTION((1.,0.,0.));
#217=IFCCARTESIANPOINT((4.440892098500626E-016,-1.776356839400251E-
015,0.));
#218=IFCDIRECTION((0.,0.,1.));
#219=IFCDIRECTION((1.,8.15911934107727E-016,0.));
#220=IFCAXIS2PLACEMENT3D(#217,#218,#219);
#221=IFCLOCALPLACEMENT(#25,#220);
#222=IFCCARTESIANPOINT((0.,0.));
#223=IFCCARTESIANPOINT((15.2,0.));
#224=IFCCARTESIANPOINT((15.2,15.2));
#225=IFCCARTESIANPOINT((0.,15.2));
#226=IFCCARTESIANPOINT((0.,0.));
#227=IFCPOLYLINE((#222,#223,#224,#225,#226));
#228=IFCARBITRARYCLOSEDPROFILEDEF(.AREA.,$,#227);
#229=IFCCARTESIANPOINT((0.,0.,0.));
#230=IFCDIRECTION((0.,0.,1.));
#231=IFCDIRECTION((1.,0.,0.));
#232=IFCAXIS2PLACEMENT3D(#229,#230,#231);
#233=IFCDIRECTION((0.,0.,1.));
#234=IFCEXTRUDEDAREASOLID(#228,#232,#233,4.6);
#236=IFCSHAPEREPRESENTATION(#14,'Body','SweptSolid',(#234));
#237=IFCPRODUCTDEFINITIONSHAPE($,$,(#236));
#238=IFCSPACE
('1Tl1VptIXFr8Crqp0zR2Pd',#19,$,'',$,#221,#237,$,.ELEMENT.,.NOTDEFINED
.,$);
#239=IFCRELCONTAINEDINSPATIALSTRUCTURE
('1CdLiZ$_X2S9yCk50MxwD6',#19,$,$,(#56,#91,#123,#155,#194,#216),#26);
#240=IFCRELAGGREGATES('3Fb1vYXv95Pwila6MRncqB',#19,$,$,#26,(#238));
#241=IFCRELAGGREGATES('0tsoDUz7TFCOzkc1xcBdbW',#19,$,$,#20,(#26));
ENDSEC;
END-ISO-10303-21;
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/CNxFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/