Re: [EnergyPlus_Support] heating/cooling at same time
Ian:
This can occur when the HVAC time step is shorter than the reporting
frequency for the report variable. If you report at the "detailed"
frequency, you will see results for every HVAC time step (they will
vary in length) and you will see how it was cooling for part of the
time and heating for part of the time during the period in question.
Mike
On 29 May 2003, at 15:46, idoebber wrote:
> Hey
>
> I am modeling a basic one zone building. When I set the thermostat to
> "Dual Setpoint with Deadband", in some of the time steps, I get both
> heating and cooling in the controlled zone. I don't understand why
> this would happen.
>
> Thanks
> Ian
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get A Free Psychic Reading! Your Online
> Answer To Life's Important Questions.
> http://us.click.yahoo.com/Lj3uPC/Me7FAA/CNxFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading!
Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/aM1XQD/od7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/