Chunming:
The real question is why is the space getting cooler than 25C? You
say it is cooler in the nighttime. Is the HVAC system supposed to be
running during this time? Is the cooling coil operating? It is
possible that the minimum airflow fraction on the VAV boxes is set
too high.
Mike
On 9 Jun 2003, at 22:33, HSIEH Chun-Ming wrote:
> Hello,
>
> I am simulating a building with water-cooled HVAC system, which is the
> same as the example of 5ZoneWaterCooled.idf. But instead, I set the
> PlantOn1 to be zero, which turns off the Heat Loop Operation (Central
> Boiler). Though the tempearture setting is 25C in the simulation, the
> mean air temperature is floating time by time during the nighttime and
> much under 25C (about 21C). Thus, I tried to turn on the PlantOn1,
> then the errors went away. I wanna ask is there any other way to fix
> the problem without turning on the Central Boiler. I hope there is no
> heating in summer in the simulation. Thank you very much.
>
> Chunming
>
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get A Free Psychic Reading! Your Online
> Answer To Life's Important Questions.
> http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Looking for the latest Free IT White Papers?
Visit SearchSecurity.com to access over 500 white papers.
Get instant access at SearchSecurity.com Today
http://us.click.yahoo.com/ayjvfD/QLNGAA/uitMAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/