Mohit:

Yes, the COMIS model in EnergyPlus should be able to model the flow 
from lower floors to upper floors as long as you use only cracks for 
the openings between floors, no large *horizontal* openings.  

Mixing extract fans with the COMIS model is a more difficult thing to 
model.  When the COMIS model is active, the MIXING, CROSS-MIXING, and 
VENTILATION objects are disabled.  The only way to force airflow in 
the building when using the COMIS model is to use an HVAC system.

Mike


On 1 Jul 2003, at 19:45, Mohit Mehta wrote:

> 
> suggestions please:
> 
> large veritcal openings can have air flow moving simultaneously in two
> different directions depending on stack effects and wind conditions
> (for eg. flow from inside to outside at the top of a window, and from
> outside to inside at the bottom) - I/O manual (energyplus)
> 
> CAN it also suggest/model that air be coming in from vertical openings
> on the lower floors and moving up a stack (modeled as large cracks) to
> exit out the tower/chimney or one of the top floors if stack
> effect/wind pressures are not conducive??
> 
> i am also trying to see if this high mass section (attached) will run
> passively in a given climate or whether an installation of extract
> fans be required at certain times to facilitate air flow from the
> perimeter openings at the lower levels. WOULD this be possible in
> EnergyPlus (COMIS). if yes, then how reliable would the results be?
> 
> thank you, ~mohit  
> 
> 
> 
> ---------------------------------
> Do you Yahoo!?
> SBC Yahoo! DSL - Now only $29.95 per month!
> 
> [Non-text portions of this message have been removed]
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get A Free Psychic Reading! Your Online
> Answer To Life's Important Questions.
> http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/