Hailey:
There is no implicit accuracy problem in the simulation for buildings 
with low HVAC loads.  The primary issue for such buildings is that 
the results become very sensitive to the building envelope and 
internal gain characteristics.  Envelope U-values as-built are often 
not as specified and infiltration is highly variable.  If trying to 
match the performance of an existing building, it may be necessary to 
measure the building's actual properties.  If trying to evalute a new 
design, several cases should be run to try and bound the problem 
using reasonable high and low values for parameters which are not 
known precisely.  
Mike
On 3 Jul 2003, at 0:58, c_l_hailey wrote:
> I have been doing some research into the accuracy of simulation 
> programs on more innovative buildings.  Particularly, well-build
> residential buildings with A LOT of passive solar design incorporated,
> therefore requiring a minimal amount of mechanical HVAC.  These
> simulations seem to have exceptionally high margin of error when
> compared to theactual energy consumption.  Do you know if there is any
> relationship?  Does EnergyPlus not respond well to buildings with a
> HVAC system which only consumes say 30% of the structures energy?  
> 
> BTW - I am not very experienced with modeling, so I cannot tell you if
> there is error in the inputs of the models I am looking at.
> 
> Thanks
> 
> Hailey
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get A Free Psychic Reading! Your Online
> Answer To Life's Important Questions.
> http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 
========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
 
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/