Part of the problem may be the autosizing. The autosizing algorithms
do not account for the presence of OA treatment equipment such as
heat recovery and desiccant dehumidifiers. You will need to
determine the DX coil size manually. If you cannot get this to work,
please send the input file as a zipped attachment to energyplus-
support@xxxxxxxx
Mike
On 22 Jul 2003, at 20:28, zhaicq98 wrote:
> I have a DX VAV system, similiar to the example file
> 5ZoneAutoDXVAV.idf. I also have an enthalpy wheel and a desiccant
> wheel on the outside air loop. When I put the enthalpy wheel after the
> desiccant wheel, the file works well. But when I make the air go
> through enthalpy wheel before it enters into desiccant wheel, an error
> messager comes up, which says "Iteration limit exceeded calculating DX
> unit compressor speedDX COOLING COIL SYSTEM 1". In addition, it
> happens in May. It runs well during the first 4 months. I do not know
> what is wrong with the coil. What I guess is that the coil can not
> handle such hot and dry air. But I am not sure, and also I do not know
> what I can do to correct it. By the way, I use autosize for the DX
> coil.
>
> Thanks,
> Chaoqin
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/sOykFB/k9VGAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/sO0ANB/LIdGAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/