Re: [EnergyPlus_Support] If there's no surface between two zones.
You are correct. If there is no surface defined, there will be no
exchange between the two zones. CROSS MIXING is a good solution for
this case. The difficult thing it to determine what the flow rate
should be for CROSS MIXING. I would recommend trying a range of
values to determine how sensitive the results are to this value.
I do not know of a way to model an air curtain in EnergyPlus.
Mike
On 23 Jul 2003, at 20:46, waspoorboy wrote:
> For example, a shopping mall has two HVAC systems. One serves the
> north half of the mall, the other serves the south half of the mall.
> The two control thermostats, one in the north zone, the other in the
> south zone, respectively. There is actually no surface between the
> north and south zone. If I didn't define a surface between two zones,
> EnergyPlus will assume no heat transfer between the two zones, am I
> correct ? In the real mall, however, there will be heat transfer
> between the north and south zone. Is CROSS MIXING the typical solution
> to this ?
>
> If the main entrance of the mall has air curtain, can I model the air
> curtain in EnergyPlus ? Thanks a lot.
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Breakthrough Natural Health Specialties
> at VitaminBoost.com $20 to $40 Naturally Painless Spray, Coral
> Calcium, No Snore, EZ Appetite Suppressant.
> http://www.challengerone.com/t/l.asp?cid=2882
> http://us.click.yahoo.com/yoMABA/ruYGAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/sO0ANB/LIdGAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/