Christian:

If you want to put a constant (or scheduled) cooling load into a 
zone, you can use OTHER EQUIPMENT and set the design value to a 
negative number.  If you want to control the space to a specified 
temperature, the easiest system to use is PURCHASED AIR (see the 
PurchAir.idf example file).  

Mike



On 13 Aug 2003, at 16:07, Christian wrote:

> Hello,
> 
> I'm searching for the easiest way to build air-condition in my zone. I
> received the information from the engineer who executes the
> construction that they will install a cold-box into the zone (only one
> room) with a cooling achievement of 3000 W.
> 
> Is there a possibility to reduce the thermal gain by this achievement
> (such as a negative space gain by electrical equipment)?
> 
> Best regards,
> 
> Christian Eulitz
> staatl. gepr. Umweltschutztechniker
> -----------------------------------------
> Möhler + Partner Beratende Ingenieure für Schallschutz und Bauphysik
> ----------------------------------------- Kopernikusstraße 7 D - 85609
> Aschheim Germany Tel. +49(0)89 90490272 e-Mail c_eulitz@xxxxxxxx
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/