Hello,
The TempRiseRate is defined in the IOReference manual on page 392 in the 
new release documentation and is a user input.

 From the manual:
Field: Temp Rise Coefficient
This numeric field contains the electric chiller's temperature rise 
coefficient which is defined as the ratio of the required change in 
condenser water temperature to a given change in chilled water temperature, 
which maintains the capacity at the nominal value.  This is calculated as 
the following ratio:
TempRiseRate =  (TCEnt req - TCEnt rated)/(TELv req - TELv rated)
where:
TCEntrequired = Required entering condenser air or water temperature to 
maintain rated capacity
TCEntrated = Rated entering condenser air or water temperature at rated 
capacity.
TELvrequired = Required leaving evaporator water outlet temperature to 
maintain rated capacity
TELvrated = Rated leaving evaporator water outlet temperature at rated capacity


Thanks Richard Liesen



At 09:22 AM 9/30/2003, Wong, S L wrote:
>Dear Richard,
>
>What's the definition of TempRiseRat?
>
>lee
>
>At 12:30 PM 9/29/2003 -0500, you wrote:
> >Hello,
> > From the EPlus source code is the definition of
> >DeltaTemp.  TempCondInDesign & TempEvapOutDesign are entered by the User.
> >
> >!Calculate chiller performance from this set of performance equations.
> >!  from BLAST...Z=(TECONDW-ADJTC(1))/ADJTC(2)-(TLCHLRW-ADJTC(3))
> >!
> >         DeltaTemp= (TempCondIn   -  TempCondInDesign) / TempRiseRat &
> >                          - (TempEvapOut -  TempEvapOutDesign)
> >
> >!  from BLAST...RCAV=RCAVC(1)+RCAVC(2)*Z+RCAVC(3)*Z**2
> >!
> >          AvailNomCapRat =   CapacityRat(1) + CapacityRat(2) *
> > DeltaTemp       &
> >                                       + CapacityRat(3) * DeltaTemp ** 2
> >
> >
> >Thanks Richard Liesen
> >
> >
> >At 04:04 AM 9/26/2003, leeslwong wrote:
> > >Dear all,
> > >
> > >What is the equation to determine the delta T in the equation of
> > >Capacity Ratio Curve in Chiller:Electric?
> > >
> > >lee
> > >
> > >
> > >
> > >To unsubscribe from this group, send an email to:
> > >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > >The primary EnergyPlus web site is found at:
> > ><http://www.energyplus.gov>http://www.energyplus.gov
> > >
> > >The group web site is:
> > ><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.co
> > m/group/EnergyPlus_Support/
> > >
> > >Attachments are not allowed -- please post any files to the appropriate
> > >folder in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > >Your use of Yahoo! Groups is subject to
> > <http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/
> >
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> ><http://www.energyplus.gov>http://www.energyplus.gov
> >
> >The group web site is:
> ><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.co 
> m/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the appropriate
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to the
> ><http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/