Dear Richard,
How can define the Delta T using the data from catalogue? Have catalogue
give out the required and rated condenser and evaporator temperatures and
where can I find those data?
lee
At 08:26 AM 9/30/2003 -0500, you wrote:
>Hello,
>The TempRiseRate is defined in the IOReference manual on page 392 in the
>new release documentation and is a user input.
>
> From the manual:
>Field: Temp Rise Coefficient
>This numeric field contains the electric chiller's temperature rise
>coefficient which is defined as the ratio of the required change in
>condenser water temperature to a given change in chilled water temperature,
>which maintains the capacity at the nominal value. This is calculated as
>the following ratio:
>TempRiseRate = (TCEnt req - TCEnt rated)/(TELv req - TELv rated)
>where:
>TCEntrequired = Required entering condenser air or water temperature to
>maintain rated capacity
>TCEntrated = Rated entering condenser air or water temperature at rated
>capacity.
>TELvrequired = Required leaving evaporator water outlet temperature to
>maintain rated capacity
>TELvrated = Rated leaving evaporator water outlet temperature at rated
>capacity
>
>
>Thanks Richard Liesen
>
>
>
>At 09:22 AM 9/30/2003, Wong, S L wrote:
> >Dear Richard,
> >
> >What's the definition of TempRiseRat?
> >
> >lee
> >
> >At 12:30 PM 9/29/2003 -0500, you wrote:
> > >Hello,
> > > From the EPlus source code is the definition of
> > >DeltaTemp. TempCondInDesign & TempEvapOutDesign are entered by the User.
> > >
> > >!Calculate chiller performance from this set of performance equations.
> > >! from BLAST...Z=(TECONDW-ADJTC(1))/ADJTC(2)-(TLCHLRW-ADJTC(3))
> > >!
> > > DeltaTemp= (TempCondIn - TempCondInDesign) / TempRiseRat &
> > > - (TempEvapOut - TempEvapOutDesign)
> > >
> > >! from BLAST...RCAV=RCAVC(1)+RCAVC(2)*Z+RCAVC(3)*Z**2
> > >!
> > > AvailNomCapRat = CapacityRat(1) + CapacityRat(2) *
> > > DeltaTemp &
> > > + CapacityRat(3) * DeltaTemp ** 2
> > >
> > >
> > >Thanks Richard Liesen
> > >
> > >
> > >At 04:04 AM 9/26/2003, leeslwong wrote:
> > > >Dear all,
> > > >
> > > >What is the equation to determine the delta T in the equation of
> > > >Capacity Ratio Curve in Chiller:Electric?
> > > >
> > > >lee
> > > >
> > > >
> > > >
> > > >To unsubscribe from this group, send an email to:
> > > >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >
> > > >The primary EnergyPlus web site is found at:
> > > ><<http://www.energyplus.gov>http://www.energyplus.gov>http://www.ener
> gyplus.gov
> > > >
> > > >The group web site is:
> > > ><<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yah
> oo.com/group/EnergyPlus_Support/>http://groups.yahoo.co
> > > m/group/EnergyPlus_Support/
> > > >
> > > >Attachments are not allowed -- please post any files to the appropriate
> > > >folder in the Files are of the Support Web Site.
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >Your use of Yahoo! Groups is subject to
> > >
> <<http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/
> > >
> > >
> > >
> > >To unsubscribe from this group, send an email to:
> > >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > >The primary EnergyPlus web site is found at:
> > ><<http://www.energyplus.gov>http://www.energyplus.gov>http://www.energy
> plus.gov
> > >
> > >The group web site is:
> > ><<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo
> .com/group/EnergyPlus_Support/>http://groups.yahoo.co
> > m/group/EnergyPlus_Support/
> > >
> > >Attachments are not allowed -- please post any files to the appropriate
> > >folder in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > >Your use of Yahoo! Groups is subject to the
> > ><<http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/>Y
> ahoo! Terms of Service.
> >
> >
> >
> >[Non-text portions of this message have been removed]
> >
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> ><http://www.energyplus.gov>http://www.energyplus.gov
> >
> >The group web site is:
> ><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.co
> m/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the appropriate
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to
> <http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/
>
>
>
>Yahoo! Groups Sponsor
>ADVERTISEMENT
><http://rd.yahoo.com/M=244522.3707890.4968055.1261774/D=egroupweb/S=1705007389:HM/A=1595056/R=0/SIG=124p07ne0/*http://ashnin.com/clk/muryutaitakenattogyo?YH=3707890&yhad=1595056>2c1568.jpg
>2c15d6.jpg
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to the
><http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.
----------
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/