[EnergyPlus_Support] Thermostat/Controller/Manager difference
ZONE CONTROL:Thermostatic
CONTROLLER:SIMPLE
Set Point Manager
For Purchased Air, WindowAC, Unitary Sys, Furnace w/DX,
ZONE CONTROL:Thermostatic tells the zone equipment
when it should be available, ie. on/off.
Q1(Y/N):ZONE CONTROL:Thermostatic doesn't tell the zone
equipment whether it should run at 30% or 70% capacity.
Actually, zone equip always run at 100% capacity when "ON".
E+ determines % capacity by Runtime Fraction in the timestep.
That's why we have HVAC,"Average",DX cooling rate.
Q2(Y/N):For Purchased Air,WindowAC,UnitarySys,Furnace w/DX,
ZONE CONTROL:Thermostatic is sufficient for control,
CONTROLLER:SIMPLE & Set Point Manager are not needed.
The reason is that there's no "Plant" in these cases.
Q3(Y/N):Now I upgrade my HVAC to single duct VAV:no reheat.
only ZONE CONTROL:Thermostatic is now "not" sufficient.
It controls only the VAV terminal box (and the VAV Fan)
but not the Coil.
Q4(Y/N):The cooling coil has to be controlled.
If we don't control it, E+ assumes the chilled water
runs at max flow all the time.
Q5(Y/N):I use Purchased:Chilled Water for the Coil,
I don't need Set Point Manager if supply air temp = const.
Set Point Manager comes in when I want to reset
the supply air temp.
Thanks for helping clearify the concept.
Thanks Mike for helping with many previous questions.
Ming
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
 
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/