[EnergyPlus_Support] Re: Room is cooled (to setpoint) obviously but report gives cooling = 0
Hi, Mike, can you help me with the connection problem ?
Thanks
>idf uploaded to [Files]>[Problem_Submittals]>VAVplant_no_flow.zip
>A node diagram is also included.
>
>err file checked, no connection errors, no orphan branches.
>Thanks for the help.
>Ming
>
>> Please upload or send your idf file (zipped, to energyplus-
>> support@g...). The max iteration errors indicate that there is
>> an error in the connections in your system or invalid control
>> settings. Check the err file. Are there any node connection errors
>> or orphan branches?
>>
>> The zone/sys sensible cooling rate should be different from the
>> sensible water cooling rate. The first one is the net cooling
>> delivered to the zone. The second is the gross cooling load on the
>> coil and will include ventilation loads and fan heat load.
>>
>> Mike
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/