Re: [EnergyPlus_Support] Re: Room is cooled (to setpoint) obviously but report gives cooling = 0
Sorry it took so long to look at this. You have only one branch on
the chilled water demand side. The demand side must have an inlet
pipe. The safest way to do this is to have an inlet pipe, then a
splitter (with only one outlet branch), the cw coil branch, then a
mixer and an outlet pipe. It might work if you just add a pipe to
your CoolingCoilBranch, but I have not tested this.
Mike
On 30 Oct 2003, at 2:07, waspoorboy wrote:
> Hi, Mike, can you help me with the connection problem ?
> Thanks
>
> >idf uploaded to [Files]>[Problem_Submittals]>VAVplant_no_flow.zip A
> >node diagram is also included.
> >
> >err file checked, no connection errors, no orphan branches.
> >Thanks for the help.
> >Ming
> >
> >> Please upload or send your idf file (zipped, to energyplus-
> >> support@g...). The max iteration errors indicate that there is an
> >> error in the connections in your system or invalid control
> >> settings. Check the err file. Are there any node connection errors
> >> or orphan branches?
> >>
> >> The zone/sys sensible cooling rate should be different from the
> >> sensible water cooling rate. The first one is the net cooling
> >> delivered to the zone. The second is the gross cooling load on the
> >> coil and will include ventilation loads and fan heat load.
> >>
> >> Mike
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for your
> HP, Epson, Canon or Lexmark Printer at MyInks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/