[EnergyPlus_Support] Fanger PMV in EnergyPlus off by 0.5 ? (more results)
By increase Activity level from 1met(105W) to 1.2met(125W)
PMV then offset 0.5, but compare to Fanger's book [Fanger, 1970]
The value EnergyPlus give is still off by 0.5
[Human body area assumed 1.8m2]
==============================
#1: Activity level = 1met(105W), RH=50%, Air velocity=0.1m/s
Results:
[Summer] 0.5clo, Tin,air=MRT=24.5C, Fanger PMV=-0.55
[Winter] 0.9clo, Tin,air=MRT=22.0C, Fanger PMV=-0.49
Fanger's book: page 116 Activity level=60kcal/m2hr=51.2W/m2=0.88met
clo Temp PMV
0.5 24 -0.20
0.5 26 +0.39
Fanger's book: page 117 Activity level=70kcal/m2hr=60.2W/m2=1met
clo Temp PMV
0.5 22 -0.33
0.5 24 +0.17
==============================
#2: Activity level = 1.2met(125W), RH=50%, Air velocity=0.1m/s
Results:
[Summer] 0.5clo, Tin,air=MRT=24.5C, Fanger PMV=-0.06
[Winter] 0.9clo, Tin,air=MRT=22.0C, Fanger PMV=-0.03
Fanger's book: page 118 Activity level=80kcal/m2hr=68.8W/m2=1.2met
air velocity = 0.1m/s
clo Temp PMV
0.5 22 -0.03
0.5 24 +0.41
................<---T=24.5, PMV=0.5
0.5 26 +0.85
==============================
#3: Activity level = 1.2met(125W), RH=50%, Air velocity=0.15m/s
Results:
[Summer] 0.5clo, Tin,air=MRT=24.5C, Fanger PMV=-0.205
[Winter] 0.9clo, Tin,air=MRT=22.0C, Fanger PMV=-0.14
Fanger's book: page 118 Activity level=80kcal/m2hr=68.8W/m2=1.2met
air velocity = 0.15m/s
clo Temp PMV
0.5 22 -0.16
0.5 24 +0.30
................<---T=24.5, PMV=0.4
0.5 26 +0.76
==============================
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/