Re: [EnergyPlus_Support] misunderstood fatal error about pump



The first branch must be the supply side inlet branch and the first 
component on this branch must be the pump.  If you are unable to get 
rid of the error, please send the input file (zipped) to energyplus-
support@xxxxxxxx or upload it to the problem files area in the yahoo 
group.  

Mike


On 14 Nov 2003, at 13:34, roblollini wrote:

> I'm simulating a building with three termal zone and a 
> central "simple boiler".
> This is the message of fatal error:
> " Fatal  ** The following pump is not the first component on its loop:
> HW CIRC PUMP" I have controlled the Branch list and the inlet an
> outlet node and it seems to me the pump is the first component of the
> supply side. Why this fatal error.
> 
> thanks a lot
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for your
> HP, Epson, Canon or Lexmark Printer at MyInks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/