Re: [EnergyPlus_Support] Consumption equation



It is difficult to reduce the problem to a simple equation.  In your 
representation the pump efficiency is misplaced.  The pump adds heat to the 
loop between the radiant system and the boiler.  So, in your terms, the 
equation would be:  

Consumption = [(total heat loss - total heat gain)/radiant system efficiency - 
pump heat]/boiler efficiency 

Mike

On 23 Jan 2004, at 8:50, meig81 wrote:

> On 21 Jan 2004, at 15:26, meig81 wrote:
> 
> > Could you write me the general equation EnergyPlus uses to calculate
> > fuel consumption?
> > I didn't find it into Engeneering Reference.
> > Thank you very much,
> > Ale
> >
> 
> ------------------------------------
> 
> Are you asking for a specific type of equipment?
> 
> -------------------------------------
> I want to know in that way energyplus holds account of the efficiency 
> of the boiler,radiant system, pump .......and so on.
> For being clearer about my question:
> Consumption = (Total heat loss - Total heat gain)/(boiler efficiency 
> * radiant system efficiency * pump efficiency)
> is it quite correct?
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
>  -- please post any files to the appropriate folder in the Files are of the
>  Support Web Site.
> 
> 
> 
> 
> 
> 
> Yahoo! Groups Links
> 
> To visit your group on the web, go to:
>  http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> To unsubscribe from this group, send an email to:
>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> Your use of Yahoo! Groups is subject to:
>  http://docs.yahoo.com/info/terms/ 
> 


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Yahoo! Groups Links

To visit your group on the web, go to:
 http://groups.yahoo.com/group/EnergyPlus_Support/

To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

Your use of Yahoo! Groups is subject to:
 http://docs.yahoo.com/info/terms/