Re: [EnergyPlus_Support] performance curves of York units
True, the z values are normalized and dimensionless, but the x and y values for
many of the curves are temperatures, in degrees C in EnergyPlus, and typically
in degrees F in DOE-2. That is where the problem comes in. Because of the 2-
part conversion between C and F, this cannnot be corrected with a simple
multiplier on the coefficients, it becomes an algebraic mess. So, it is
easiest to just do the curve-fit using x and y values in deg. C. DOE-2 will
not care that the values are in deg. C as long as you are just running the
curve fit and not trying to do a simulation with the data.
Mike
On 25 Feb 2004, at 14:53, Chris Jones wrote:
> Correct me if I am wrong but with DOE-2 you have to normalize the data
> points before you use the DOE-2 curve fit command. Regardless of the units used
> to determine the normalized data points, the curve is the same shape?
>
>
>
> >Another user suggested using DOE-2 to do the curve fit. If you do that, you
> >have to be very careful about units conversions. You would need to enter the
> >values as SI values in the DOE-2 curve fit command.
> >
> >Mike
> >
> >
> >On 25 Feb 2004, at 12:46, Edward Lyon wrote:
> >
> > > I think you may need the math power of MathCad to do a biquadratic easily,
> > > otherwise you will need to program a solution yourself.
> > >
> > > Ned Lyon
> > >
> > > Senior Project Manager
> > > Simpson Gumpertz & Heger Inc.
> > >
> > > 41 Seyon Street
> > > Building #1, Suite 500
> > > Waltham, MA 02453
> > >
> > > Phone: 781-907-9000
> > > Fax: 781-907-9009
> > >
> > >
> > > >>> dcormier81@xxxxxxxxxxx 2/24/2004 8:29:06 AM >>>
> > > yes, excel do a good job for quadratic curve .... but the
> > > biquadratic?????????
> > >
> > > if you are able to make biquadratric (f(x,y)) curve with, tell me how ...
> > >
> > > david
> > >
> > >
> > > >From: ÕŹâÓñ <zh_guangyu@xxxxxxxxxxxx>
> > > >To: dcormier81@xxxxxxxxxxx
> > > >Subject: Re: [EnergyPlus_Support] performance curves of York units
> > > >Date: Tue, 24 Feb 2004 09:55:01 +0800 (CST)
> > > >
> > > >if you can input the data into excell work sheet, then it is easy to
> > find the
> > > >vurve. by using curve fitting, you quickly get the curve
> > > >
> > > >
> > > >
> > > >---------------------------------
> > > >Do You Yahoo!?
> > > >ÍêÈ«Ãâ·ÑµÄÑÅ»¢µçÓÊ£*ÂíÉÏ×¢²á»ñÔù¶îÍâ60Õ×ÍøÂçæ¢¿Õ¼ä
> > >
> > > _________________________________________________________________
> > > MSN Search, le moteur de recherche qui pense comme vous !
> > > http://fr.ca.search.msn.com/
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the appropriate
> > folder
> > > in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > > -- please post any files to the appropriate folder in the Files are of the
> > > Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > Yahoo! Groups SponsorADVERTISEMENT
> > > Click Here
> > > Yahoo! Groups Links
> > > To visit your group on the web, go to:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the appropriate
> > folder
> > > in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > > -- please post any files to the appropriate folder in the Files are of the
> > > Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> >
> >
> >
> >========================================================
> >Michael J. Witte, GARD Analytics, Inc.
> >EnergyPlus Testing and Support
> >EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the appropriate
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> > -- please post any files to the appropriate folder in the Files are of
> > the Support Web Site.
> >
> >
> >
> >
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
>
>
> Chris Jones, P. Eng.
> 14 Oneida Avenue
> Toronto, ON M5J 2E3
> Tel. 416 203-7465
> Fax. 416 946-1005
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of the
> Support Web Site.
>
>
>
>
>
> Yahoo! Groups Links
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/