LINEST is going to give you a straight line fit to the data in the colums, not the coeficients of a bi-quadratic fit to the data

Ned Lyon

Senior Project Manager
Simpson Gumpertz & Heger Inc.

41 Seyon Street
Building #1, Suite 500
Waltham, MA  02453

Phone:  781-907-9000
Fax:  781-907-9009


>>> mjwitte@xxxxxxxx 2/25/2004 1:23:43 PM >>>
Excel can curve fit any form of an equation using the LINEST function if you 
creat extra columns of data to represent the non-linear terms.  For example, to 
curve-fit a bi-quadratic, z=A+Bx+Cx2+Dy+Ey2+Fxy, make six columns of data in 
Excel containing values for x, x2, y, y2, xy, and z.  Then use LINEST to 
curvefit z vs. the other five columns.

Another user suggested using DOE-2 to do the curve fit.  If you do that, you 
have to be very careful about units conversions.  You would need to enter the 
values as SI values in the DOE-2 curve fit command.

Mike


On 25 Feb 2004, at 12:46, Edward Lyon wrote:

> I think you may need the math power of MathCad to do a biquadratic easily,
> otherwise you will need to program a solution yourself.
> 
> Ned Lyon
> 
> Senior Project Manager
> Simpson Gumpertz & Heger Inc.
> 
> 41 Seyon Street
> Building #1, Suite 500
> Waltham, MA  02453
> 
> Phone:  781-907-9000
> Fax:  781-907-9009
> 
> 
> >>> dcormier81@xxxxxxxxxxx 2/24/2004 8:29:06 AM >>>
> yes, excel do a good job for quadratic curve .... but the 
> biquadratic?????????
> 
> if you are able to make biquadratric (f(x,y)) curve with, tell me how ...
> 
> david
> 
> 
> >From: ÕŹâÓñ <zh_guangyu@xxxxxxxxxxxx>
> >To: dcormier81@xxxxxxxxxxx 
> >Subject: Re: [EnergyPlus_Support] performance curves of York units
> >Date: Tue, 24 Feb 2004 09:55:01 +0800 (CST)
> >
> >if you can input the data into excell work sheet, then it is easy to find the
> >vurve. by using curve fitting, you quickly get the curve
> >
> >
> >
> >---------------------------------
> >Do You Yahoo!?
> >ÍêÈ«Ãâ·ÑµÄÑÅ»¢µçÓÊ£*ÂíÉÏ×¢²á»ñÔù¶îÍâ60Õ×ÍøÂçæ¢¿Õ¼ä
> 
> _________________________________________________________________
> MSN Search, le moteur de recherche qui pense comme vous !  
> http://fr.ca.search.msn.com/ 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov 
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/ 
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
> -- please post any files to the appropriate folder in the Files are of the
> Support Web Site.
> 
> 
> 
> 
> 
> 
> 
> Yahoo! Groups SponsorADVERTISEMENT
> Click Here
> Yahoo! Groups Links
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/ 
>   To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
>   Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov 
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/ 
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
>  -- please post any files to the appropriate folder in the Files are of the
>  Support Web Site.
> 
> 
> 
> 
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx 



The primary EnergyPlus web site is found at:
http://www.energyplus.gov 

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ 

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




-- please post any files to the appropriate folder in the Files are of the Support Web Site.







Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/ 
  To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/