Re: [EnergyPlus_Support] control dampers



I am not sure I understand exactly what your bypass will do.  The dual duct and 
VAV dampers are controlled by the zone thermostat to meet the zone setpoint.  
The central heating coil in such a system is controlled by a setpoint manager 
to meet a specified leaving air temperature off the coil.  See the 
DDAutoSize.idf and 5ZoneAuto.idf example files.

Mike


On 1 Mar 2004, at 20:13, David Cormier wrote:

> hello,
> 
> I have a second interrogation about the control of damper ... I model a 
> central heating coil with a constant fan ... I want to have a damper in the zone
> and a big bypass that will take the flow that the damper will not take ....
> 
> May I use SINGLE DUCT:CONST VOLUME or SINGLE DUCT:VAV ?
> 
> How the program proceed to choose if he open the damper or increase the coil
> production ?? How we can control that choice ??
> 
> (I look at the example files of vav ... I don't see damper control...)
> 
> thank you!
> 
> david cormier
> 
> _________________________________________________________________
> MSN Messenger : discutez en direct avec vos amis !  
> http://messenger.fr.msn.ca/
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
>  -- please post any files to the appropriate folder in the Files are of the
>  Support Web Site.
> 
> 
> 
> 
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/