[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] warm-up time
hi:
since EPlus uses the first day of the simulation to perform its warm-up till it reaches convergence and then simulates for the rest of the days - is there any way of controling this warm-up period/time...? can one enter ZERO warm-up days...?
OR as ned mentioned - use a cool period before the hotter days to see how my building responds to a quick warm-up (is the only way). as this will require altering the weather file...!
thank you,
~m
Rick Strand <rkstrand@xxxxxxxx> wrote:
As Ned and Dru have already mentioned, E+ does have a warmup period during
which the program will iterate on the same day until it reaches
"convergence". For a design day environment, E+ will use the design day
and repeat it until it reaches "steady periodic" conditions. For a weather
environment, E+ will use the first day of the weather file for the warmup
period. Once convergence is reached in any of these cases, it will then
start the simulation time clock. Note that it reinitializes temperature
histories between different weather environments (individual design days or
weather files) to the same starting initial condition before it starts the
iterative warmup process.
As Ned suggested, if one wants to see how the building reacts to several
days of extreme conditions, add an additional "normal" day to the weather
period. The results should show the temperatures/loads drift, with the
amount of drift obviously a function of building type, materials, location,
weather, etc.
Rick Strand
At 08:53 AM 3/11/2004, Edward Lyon wrote:
>As I understand the startup of an E+ calculation, the program must
>iterate to a repeatable starting condition before moving into the actual
>calculation. Consequently, if you try to model single days (like just a
>design day), your model will always look like the conditions have been
>the same for a long time. To see what you want, you probably need to
>calculate several days with the first days being your cool weather and
>the last days being your hot weather. You should then see the building
>respond to a quick warmup.
>
>Ned Lyon
>
>Senior Project Manager
>Simpson Gumpertz & Heger Inc.
>
>41 Seyon Street
>Building #1, Suite 500
>Waltham, MA 02453
>
>Phone: 781-907-9000
>Fax: 781-907-9009
>
> >>> mohitmehta1@xxxxxxxxx 03/11/04 12:38 AM >>>
>
>hi:
>
>if am running a simulation of a high mass NV building between aug 14 -
>17 (4 hot days) - shouldn't the building take a few hours or days to
>warm up? like indoor and outdoor temperatures starting out the same on
>the first day (aug 14), and indoor air temperatures climbing gradually
>over the four-day period; finally balancing out? it appears that the
>mass starts out as preheated (warmed/cooled). does it use 3-4 warm-up
>days before the days that i am looking at are reported?
>
>thank you.
>
>~m
>
>
>---------------------------------
>Do you Yahoo!?
>Yahoo! Search - Find what you
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of
> the Support Web Site.
>
>
>
>
>
>Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
Do you Yahoo!?
Yahoo! Mail - More reliable, more storage, less spam
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/