Re: [EnergyPlus_Support] Question: Radiant Panel
You have two options, embed the heater in your wall surface(s) or add a new
surface within the zone. If you add it to your wall surface, you may want to
break the wall into two surfaces to represent the portion with the radiant
panel and the portion without. In any low-temp radiant surface, you must place
at least one layer of material over the internal source. Peter A. cautions
against using a metal layer in the construction. I believe those problems have
been fixed, however, you should check the behavior carefully. If you run into
problems, try a thin layer of gypsum or concrete instead.
Mike
On 18 Apr 2004, at 20:31, zhen tian wrote:
> Hi, Mike:
>
> Could you tell me how to define the " near the inside face of the surface and a
> very thin layer of material on top of it" ?
>
> I do not know how to define it. Should I add another surface and then define it
> as thin construction with internal source?
>
>
> Thanks.
>
> David Tian
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> You have two options:
>
> 1) Baseboard Heater:Water:Convective which is thermostatically controlled and
> adds heat to the space by convection.
>
> or 2) Use LOW TEMP RADIANT SYSTEM:HYDRONIC with the source near the inside face
> of the surface and a very thin layer of material on top of it.
>
> Mike
>
>
> On 15 Apr 2004, at 23:32, tianzhen9 wrote:
>
> > Hi, there,
> >
> > I am modelling the radiant cooling slab system with perimeter
> > radiant panel heating system.
> >
> > I can not find the "hydraulic radiant panal system" in Energyplus.
> > It sounds like somebody has posted this question before, but I
> > cannnot find it.
> >
> > Should I set the "Radiant Panel" as "Baseboard Heater:
> > Water:Concective"? And how about other directions?
> >
> > Thanks a lot.
> >
> > David Tian
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups SponsorADVERTISEMENT
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Photos: High-quality 4x6 digital prints for 25ยข
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/