Re: [EnergyPlus_Support] ceiling, adiabatic surface or not?
The reason the first level is warmer than the top floor is because of the
floor, which I presume has an outside environment of ground and the ground
temperatures are much warmer than -21C. When you allow heat transfer between
the levels, then more heat flows out of the first level and thus it balances
out at a cooler temperature. So your results look reasonable for an
unconditioned building.
Mike
On 4 May 2004, at 23:54, teklay Weldeabzgi wrote:
> you can take ceilings as an adiabatic if you set the
> indoor tempereture of the space above and below the
> ceiling is the same. otherwise you should cnsider heat
> transfer through ceilings if the temperature of the
> storise are differrent.
>
> in short you can take surfaces as adiabatic if the
> surface is in one zone, else take the surface as heat
> transfer surface if it separates two different thermal
> zones.
> --- pizzaalan <pizzaalan@xxxxxxxxx> wrote:
> > Thank you very much for those who helped me before.
> >
> > I simulated 3 story building without adding any HVAC
> > system first.
> > If I set all ceilings between any two stories to
> > adiabatic walls,
> > then mean air temperature of third floor is close to
> > outside
> > environment temperature. Say outdoor temperatue is
> > -21 C, then mean
> > air temperature of first level is 18 C, second level
> > is -2 C, the
> > third level is -20 C.
> >
> > If I add the heat transfer between each story by
> > setting that each
> > ceiling's outside surface environment object is
> > floor of its upper
> > level, then now outdoor temperatue is still -21 C,
> > mean air
> > temperature of first level is 15 C, second level is
> > 9 C, the third
> > level is 5 C.
> >
> > Should mean air temperature of each story be very
> > close? Should I
> > view ceilling as an adiabatic surface or not?
> >
> > Thanks again.
> >
> > Alan
> >
> >
> >
> > ------------------------ Yahoo! Groups Sponsor
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files
> > to the appropriate folder in the Files area of the
> > Support Web Site.
> >
> > Yahoo! Groups Links
> >
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >
> >
>
>
>
>
>
> __________________________________
> Do you Yahoo!?
> Win a $20,000 Career Makeover at Yahoo! HotJobs
> http://hotjobs.sweepstakes.yahoo.com/careermakeover
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/