Re: [EnergyPlus_Support] Question: Simulation Time
Yes, the iteration errors are causing the long run time, especially in a
buildin as large and complex as yours. Maximum iteration errors are usually
related to mass flow or temperature problems around the loop. This occurs when
the air loop side is doing something contrary to the zone equipment. Examples
of situations which may cause this include: sum of peak terminal unit airflows
does not equal the peak supply fan air flow, node connection errors, bad
control nodes, incorrect use of active and passive branches, inconsistent
equipment schedules, and inconsistent control setpoints.
Mike
On 6 May 2004, at 19:18, zhen tian wrote:
> Hi,All:
>
> I have a question for the simulation time. I am simulating a big university
> building. I just do two-days simulation and it takes hours to run and there
> will be warning "Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, at CALGARY INT'L AB CAN WYEC2-B-25110 WMO#=718770, 01/02 09:45 - 09:52"
> and "Warning ** SimHVAC: Exceeding max iterations continues...250" . This
> warning continues until the end of the simualtion day. Is this problem causes
> such a long time simulation time?
>
> Could anybody tell me that which parameter causes this problem and how can I
> solve it?
>
> Thanks.
>
> David Tian
>
>
> ---------------------------------
> Do you Yahoo!?
> Win a $20,000 Career Makeover at Yahoo! HotJobs
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/