Re: [EnergyPlus_Support] economizer



That is controlled by the next two fields "ReturnAirTempLimit" and 
"ReturnAirEnthalpyLimit". See the Input Output Reference, p. 759 (pdf p. 786 
for more details.

Mike

On 14 May 2004, at 19:10, zl21e wrote:

> In "controller:outside air", there is a choice of using economizer.  
> Is this economizer based on enthalpy or temperature?  Thank you!
> 
> Li Zhang
> 
> 
> 