FURNACE:BLOWTHRU:HEATCOOL operates with a single flow rate for both heating and
cooling. You must model two systems, one for heating and one for cooling to
have different flow rates. Because a given zone may be served by only one AIR
PRIMARY LOOP, the second system must be a piece of zone equipment, such as AIR
CONDITIONER:WINDOW:CYCLING or UNIT HEATER.
Mike
On 18 May 2004, at 11:49, Ian Doebber wrote:
> I am using the "FURNACE:BLOWTHRU:HEATCOOL" unitary system and was wondering
> whether I could specify one flow rate for the cooling operation and a different
> flow rate for the heating operation. Is this possible or can this type of
> system only be specified at one flow rate. If I can not specify 2 flow rates
> for this system, is there another unitary system that I can do this for or do I
> have to creating two seperate systems, one for heating and one for cooling.
>
> Thanks
> Ian Doebber
> Graduate Student
> Mechanical Engineering
> Virginia Tech
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/