[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Flow rate
No. It uses the design days to determine the peak loads, and then it will a
whole year (RunPeriod) using the autosized values. See the RUN CONTROL object
for details.
Mike
On 3 Jun 2004, at 13:08, Meng Zhang wrote:
> Hi, Michael,
>
> Thank you for your help. I am thinking to use "zone, system and plant sizing" to
> get the flow rates. Do you think it is possible? It seems that "sizing " is
> just for design days. If I want to run system like a whole year, I have to
> specify all the flow rates by hand. Is it right?
>
> Sincerely,
> Alan
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> The max flow rate in the air loop main branch is usually set to equal the sum of
> the max flow rates of the terminal units. In your case, if you air loop serves
> a single zone, then the max flow rate should equal the max damper air flow rate
> of 0.47 m3/s. The fan max flow rate should be the same. The fan min flow rate
> is set by the min flow rate of the terminal untis. This is all just continuity.
> Look at your system diagram and once you know the flow rates of the terminal
> units, then you can figure out the flow rates for the other components. Or you
> can use the sizing features to set these values for you.
>
> Mike
>
>
> On 2 Jun 2004, at 9:03, pizzaalan wrote:
>
> > Hi,
> >
> > I am not sure how to choose max flow rate for air loop main branch,
> > (1.3 m3/s in example), max plant loop volumetric flow rate (0.0011
> > m3/s in example), max damper air flow rate (0.47 m3/s).
> >
> > Also, I am not sure how to pick up pump ( pump head? rated
> > volumetric flow rate), Fan max & min flow rate?
> >
> > I will appreciate if anyone gives me a guide. Thanks.
> >
> > Alan
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups SponsorADVERTISEMENT
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Friends. Fun. Try the all-new Yahoo! Messenger
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/