All of the materials in this building are MATERIAL:REGULAR-R which have no 
thermal mass.  All materials which are not lightweight insulation should be 
defined with MATERIAL:REGULAR to add mass to the simulation.

Even with this change, the building is likely to overheat, because there are 
windows, but no infiltration and no HVAC system.  I recommend that you add 
purchased air to condition your zones.  See the PurchAir example file for 
details on how to do this.

Mike


On 1 Jun 2004, at 14:49, Michael J. Witte wrote:

> 1. I need to see your input file in order to help you with the temperature
> error. 2.  A single surface can only see one zone on either side.  If the floor
> of one zone is the ceiling of two or more zones below, then you are correct that
> the surface must be divided into two or more floor surfaces.
> 
> Mike
> 
> 
> On 31 May 2004, at 15:58, leila wrote:
> 
> > Hi,
> > 
> > I need help to solve a fatal error. Without solving it i can´t 
> > continue working.
> > 
> > 
> > ** Severe  ** Temperature out of bounds (-108.88) for surface=PISO 
> > 04:ZN001 CHÃO 1 occuring in simulation=CHICAGO IL USA TMY2-94846 
> > WMO#=725300 at 03/26 15:10 A temperature out of bounds problem can be 
> > caused by several things.  The user should check the weather 
> > environment, the level of internal gains with respect to the zone, 
> > and the thermal properties of their materials among other things.
> > ** Fatal  ** EnergyPlus has exited due to the reason stated above
> > 
> > 
> > I have one more question:
> > I´m simulating a several floors building, i need to know if i need to 
> > divide each ceiling of several zones to correspond to the floor of 
> > other zone.
> > 
> > Leila Félix Henriques (portuguese student)
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/