Re: [EnergyPlus_Support] help me to solve this problem



In the ZONE CONTROL:THERMOSTATIC object, the Control Type Schedule must be 
consistent with the types of thermostats that are used.  If you are only using 
"Single Cooling SetPoint", then the control type schedule should contain only 2 
or 0.  For more explanation, see the Input Output Reference, p. 630 (pdf p. 
658).

Mike


On 5 Jun 2004, at 19:40, Xu H.T wrote:

>   Dear,
> 
>   I do a simple simulation for a HVAC system, serving a zone. Using the Hong
>   Kong weather data, only cooling is needed during the period from June to
>   Auguest. 
> 
>   There is a fatal error: Could not Find SINGLE HEATING SETPOINT Object defined
>   in IDF, a value of "1" in ZONECONSCHED for zone ZONE1
> 
>   Only cooling is needed, heating setting is also needed?
> 
>   Thanks,
> 
>   Xu 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/