Based on the last data in the csv output file, the run is terminating on 04/19
sometime between 16:00 and 17:00. The weather data for these hours is very hot
and dry 31-32C (88-90F) and RH 14%. The Dulles weather file RH never drops
below 20% RH during warm weather. I suspect that the hot dry weather may be
triggering the iteration problem. I will forward this to another team member
to determine why the DX coil model is struggling with this simulation.
Mike
On 6 Jun 2004, at 15:20, Drury.Crawley@xxxxxxxxxx wrote:
>
> Lucia,
>
> I ran your IDF with both the College Park EPW you created and the Sterling
> (Washington Dulles) EPW.
> Yes, the College Park EPW does have a fatal error but you also have a large
> number of serious errors and warnings even when running the Sterling weather.
>
> 1. You need to change your IDF version to 1.2.0 (doesn't cause a problem,
> only a warning).
>
> 2. A number of your dayschedules and schedules don't include a
> scheduletype. Inserting AnyNumber
> in these fixes the problem. (This only causes a warning.)
>
> 3. There is something wrong with your plenum surfaces... the view factors
> calculations can't complete.
> Still looking into this issue... this is the most serious error.
>
> Could you send me (directly to my email) the CSV or the .AUDIT you got when you
> converted the EPW to College Park? I didn't see any immediate problems but
> would like to what the WeatherConverter does with the original file.
>
> Dru Crawley
>
>
>
>
> "Lucia Liao"
> <liao@xxxxxxxxxxx To:
> EnergyPlus_Support@xxxxxxxxxxxxxxx >
> cc:
>
> Subject: Re: [EnergyPlus_Support]
> Weather file in College
> 06/06/2004 12:20 Park
> PM
> Please respond to
> EnergyPlus_Suppor t
>
>
>
>
>
>
>
> I just uploaded the Chesapeake_DXVAV_SA55.IDF and the weather zip file in
> College Park, MD US_CollegePark2.zip under my name ID: liao_lucia. Please
> correct the fatal error by using my weather data. The idf file works fine
> in other weather data. But I can not find anything wrong with my weather
> data.
>
> Thank you !
>
> Lucia
> ----- Original Message -----
> From: Drury.Crawley@xxxxxxxxxx
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Sent: Saturday, June 05, 2004 4:56 PM
> Subject: Re: [EnergyPlus_Support] Weather file in College Park
>
>
>
> You cannot attach files in this email list.
> Upload the file to the files area of the
> EnergyPlus_Support YahooGroup.
>
>
>
>
> "Xiaohong Liao"
>
> <liao@xxxxxxxxxxx To:
> EnergyPlus_Support@xxxxxxxxxxxxxxx
> > cc:
>
> Subject:
> [EnergyPlus_Support] Weather file in College Park
> 06/04/2004 05:43
>
> PM
>
> Please respond to
>
> EnergyPlus_Suppor
>
> t
>
>
>
>
>
>
>
> The attached file is for my previous email.
>
>
>
> Thank you !
>
>
>
> Lucia
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
>
>
>
> ADVERTISEMENT
>
>
>
>
>
>
>
>
> Yahoo! Groups Links
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service.
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
>
>
>
>
>
> ------------------------------------------------------------------------------
>
> Yahoo! Groups Links
>
> a.. To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> b.. To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service.
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
>
>
>
> ADVERTISEMENT
>
>
>
>
>
>
>
>
> Yahoo! Groups Links
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/